thanks BobO,
Bigger turbines run at 3600 RPM. They often use a 60 tooth wheel which means the HZ reading and the RPM reading are the same. The speed sensor sees 3600 teeth or pulses per second for a 60 HZ single shaft machine. Smaller turbines turn faster and so need higher HZ readings. Does your counter perform at 3600 HZ to 7000 HZ. The signals are very low VAC at low RPMs and I have seen 30 VAC at full speed. Lots of variables on the voltage, pickup, sensor gap, speed, tooth size but that's a range. there are some work arounds for poor low speed detection, timers etc.
glad you are testing this, who knows where this leads. I am open minded about using your counter card.
generally filters are a nono, a filter delays response to good signals, defeating the purpose of fast loops and can causes control instability.