News:

  • October 20, 2026, 10:41:10 AM

Login with username, password and session length

Author Topic: GSREGWR Errors with 2.7.1 upgrade  (Read 6379 times)

Bolt

  • Hero Member
  • *****
  • Posts: 598
GSREGWR Errors with 2.7.1 upgrade
« on: March 31, 2020, 11:55:24 AM »
I've had some GSREGWR instructions for years.  I think they worked as intended.  Now with my latest update, I get an error message that a few of the parameters should be a Modbus Write instead of a GSEDrive Write?  What gives?  For now I deleted the 2 offending rows, but something's still different.  Please clarify.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3852
    • Host Engineering
Re: GSREGWR Errors with 2.7.1 upgrade
« Reply #1 on: March 31, 2020, 12:19:33 PM »
Yes.  P9.x parameters are not write-able via GSREGWR since those are communication parameters.  It never reported an error, but the values never got written either, so the logic was always "not working".

If you do need to configure specific Comm parameters at startup, use MWX and write to those parameters via Modbus.  GSREGWR uses the "block transfer" method, which dis-allows P9.x parameters.  If you use Modbus, you are by-passing that GSDrive "block transfer" mechanism.

Bolt

  • Hero Member
  • *****
  • Posts: 598
Re: GSREGWR Errors with 2.7.1 upgrade
« Reply #2 on: March 31, 2020, 12:21:31 PM »
Okay, thanks.  That's why I said I "think" they worked as intended.