News:

  • November 23, 2026, 06:40:56 AM

Login with username, password and session length

Author Topic: PID Controller Stopped Working  (Read 11394 times)

HennieKotze

  • Newbie
  • *
  • Posts: 1
PID Controller Stopped Working
« on: July 30, 2019, 01:20:47 AM »
Good Day,

I have recently replaced one of my D4-450 CPU's with a new D4-454 CPU. I downloaded the backup program onto it, and it all worked perfect.

After almost a month, the PID control stopped working. Right now I have to control my valves by placing the controller in manual, and adjusting the output myself. As soon as I put the controller into Auto mode, the output changes to 5 milliamps and stays there. Even if the controller shows 4095 in the output, the milliamp output on the analog output card does not change. Only If I put the controller in Manual, and and adjust the output to 100%, does the analog output card give me 20 milliamps. This has now suddenly happened on all 8 of my loops.

I trend my PV, SP and OUTPUT in the PID setup, and the controller clearly increases the output to 100% (4095). When I test my milliamp output, I only get 5 milliamps. When I put my controller in Manual mode and adjust the output to 100%, then I measure 20 milliamps on my output card.

It's weird... but now the plant operator has to control these loops in manual, so i'm desperate to find the problem quickly.


franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: PID Controller Stopped Working
« Reply #1 on: July 30, 2019, 08:01:37 AM »
I see that you figured out this issue on the Automation Direct forum https://forum.automationdirect.com/forum/general-applications/124318-pid-control-stopped-working

Glad that you got it working!