News:

  • November 23, 2026, 05:48:55 AM

Login with username, password and session length

Author Topic: MQTT Connect / Disconnect  (Read 36210 times)

Andrew S

  • Hero Member
  • *****
  • Posts: 144
MQTT Connect / Disconnect
« on: May 24, 2019, 10:41:57 AM »
Perhaps I've missed something, but I'm doing an MQTT Publish which is working fine. I noticed though that every time the command runs it connects, publishes the data, and then disconnects.

MQTT is designed to have long-running TCP connections. This is how LWT functions operate on the broker - it looks for a disorderly disconnect. The way that (to my understanding) the current implementation works, the immediate disconnect means that there's no active TCP connection for the broker to manage, and therefore process an LWT if necessary.

Usually, MQTT clients have a CONNECT and a DISCONNECT command that get issued appropriately. Is there a way to make this happen in a future release?


On a separate but related subject, would it be possible to override the default MQTT client name in a future release? I'd find this very useful.

Thanks, Andrew

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #1 on: May 24, 2019, 10:58:24 AM »
You are either dropping the Enable leg or you are terminating the containing code block. The connection is maintained as long as at least one instruction is enabled, and automatically closed when the last instruction is disabled.

It should be fairly easy to add a DEVWRITE property to override the client name.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #2 on: May 24, 2019, 12:16:01 PM »
Okay. That helps. Thanks Bob.

Andrew.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #3 on: May 24, 2019, 12:21:21 PM »
Okay. That helps. Thanks Bob.

Andrew.

For folks like yourself who are intimately acquainted with the implementation details of MQTT, we probably wouldn't have approached it that way, instead preferring a full API with individual instructions for connecting, disconnecting, etc. The reality is that vast majority of our users just want to make MQTT work, with zero insight into the sausage making process.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #4 on: June 23, 2019, 12:45:48 AM »
It should be fairly easy to add a DEVWRITE property to override the client name.

Did this make it into 2.6? I don't see it as a property in the GUI or the help docs.

Andrew.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #5 on: June 23, 2019, 10:46:33 AM »
It should be fairly easy to add a DEVWRITE property to override the client name.

Did this make it into 2.6? I don't see it as a property in the GUI or the help docs.

Andrew.

It didn't. I'm sorry. Just added...it'll be in 2.7.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #6 on: June 24, 2019, 01:16:10 AM »
Thanks Bob.

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #7 on: June 30, 2019, 04:21:30 PM »
Bob, I'm still struggling with the CONNECT/DISCONNECT issue. The current design seems sensible but since I'm using Stage programming I think that's causing issues.

I have a project that uses a FIFO to send data via MQTT. If the Publish fails it runs a timer for 30 seconds then retries until successful. I'm finding that if the broker is down and the FIFO starts to fill, on reconnect the PLC attempts to publish each message as desired, but only every other message makes it to the broker. This might be a timing thing but the messages that get lost show in Logger as being processed during MQTT Disconnect. All very strange.

Since each individual message is connecting, publishing and then disconnecting, I still have the original concern about LWT processing not functioning properly.

Is there a way I can program this so that it works properly or do I need to request again that you add CONNECT and DISCONNECT functionality?

Logger output is below (latest at the top). I can email you the program export if necessary.

Thanks, Andrew.

---- LOGGER STARTS ----
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.799 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.798 ,"MQTT disconnected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.797 ,"Disconnecting MQTT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.745 ,"Sending DISCONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.743 ,"Stage S20 / 5 / 0 / 1561924365 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.740 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.739 ,"PUBACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.737 ,"Sending PUBLISH for V2/TEST/4"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.736 ,"CONNACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.733 ,"Sending CONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.729 ,"MQTT broker connected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.728 ,"Connecting to MQTT broker..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.721 ,"Stage S20 / 4 / 0 / 1561924364 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.721 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.720 ,"MQTT disconnected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.719 ,"Disconnecting MQTT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.648 ,"Sending DISCONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.648 ,"Stage S20 / 2 / 0 / 1561924363 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.647 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.646 ,"PUBACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.646 ,"Sending PUBLISH for V2/TEST/3"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.645 ,"CONNACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.645 ,"Sending CONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.644 ,"MQTT broker connected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.644 ,"Connecting to MQTT broker..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.643 ,"Stage S20 / 3 / 0 / 1561924362 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.643 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.642 ,"MQTT disconnected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.641 ,"Disconnecting MQTT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.502 ,"Sending DISCONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.501 ,"Stage S20 / 1 / 0 / 1561924362 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.501 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.499 ,"PUBACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.498 ,"Sending PUBLISH for V2/TEST/5"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.497 ,"CONNACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.495 ,"Sending CONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.493 ,"MQTT broker connected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.492 ,"Connecting to MQTT broker..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.490 ,"Stage S20 / 5 / 1 / 1561924360 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.489 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.487 ,"MQTT disconnected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.485 ,"Disconnecting MQTT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.413 ,"Sending DISCONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.412 ,"Stage S20 / 4 / 1 / 1561924360 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.412 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.411 ,"PUBACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.411 ,"Sending PUBLISH for V2/TEST/3"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.410 ,"CONNACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.410 ,"Sending CONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.409 ,"MQTT broker connected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.409 ,"Connecting to MQTT broker..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.409 ,"Stage S20 / 3 / 1 / 1561924359 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.408 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.408 ,"MQTT disconnected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.407 ,"Disconnecting MQTT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.262 ,"Sending DISCONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.261 ,"Stage S20 / 2 / 1 / 1561924358 "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.260 ,"MQTT OK "
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.258 ,"PUBACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.256 ,"Sending PUBLISH for V2/TEST/1"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.255 ,"CONNACK received"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.254 ,"Sending CONNECT..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.253 ,"MQTT broker connected!"
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.252 ,"Connecting to MQTT broker..."
10.0.75.1  Port 29298(0x7272),06/30/19 12:53:09.251 ,"Stage S20 / 1 / 1 / 1561924358 "
---- LOGGER ENDS ----

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #8 on: June 30, 2019, 04:45:33 PM »
Can you add single dummy subscription globally, effectively a keep-alive?

Since the first item enabled will force the CONNECT, and the last item disabled will force the DISCONNECT, you can easily control that.
« Last Edit: June 30, 2019, 04:48:47 PM by BobO »
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #9 on: June 30, 2019, 05:16:03 PM »
That helped Bob. I'm losing the first PUBLISH after reconnect though (other messages seem fine). I'm thinking that it's a timing issue. It feels like the success bit is being set before the entire dialog has completed - is this possible?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #10 on: June 30, 2019, 06:16:10 PM »
That helped Bob. I'm losing the first PUBLISH after reconnect though (other messages seem fine). I'm thinking that it's a timing issue. It feels like the success bit is being set before the entire dialog has completed - is this possible?

Success and error have a slightly different meaning in comm function like this. In continuous operation, they wiggle every time a pass completes. Continuous mode isn't really compatible with Stage. In edge mode, they should turn off as soon as the edge is latched in and one turn on in response to the completion of the box. Unless it is broken, setting the result is a critical part of the box ending. MQTT boxes are kinda fickle though, because the box doesn't really do the work, it interacts with the driver.

We banged on it pretty hard, but I know I didn't do it in stage. We'll do some testing.

"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #11 on: June 30, 2019, 06:56:08 PM »
That sounds good. I was able to get the first PUBLISH out to the broker on a couple of tests so it definitely seems like a timing option. I'll leave the 1-second delay in there as a workaround. Let me know if you need me to test any further.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #12 on: June 30, 2019, 07:01:12 PM »
I created a simple test with a dedicated publishing program that reads from a FIFO. I added a single MQTTSUB to $Main and use it to connect and disconnect. I can't see that it is ever dropping the first publish following a reconnect.

I modded the program to trigger the FIFO load directly from the same bit that triggers the MQTTSUB, forcing those two operations to happen at virtually the same time. It still doesn't fail for me ever. I'm talking to a local instance of mosquitto, so it could be different off-site.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: MQTT Connect / Disconnect
« Reply #13 on: June 30, 2019, 07:02:25 PM »
Not sure why this didn't post...
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Andrew S

  • Hero Member
  • *****
  • Posts: 144
Re: MQTT Connect / Disconnect
« Reply #14 on: June 30, 2019, 07:28:40 PM »
It all seems to work fine if the broker's there. Try shutting the broker down, stick a bunch of things in the queue, then see what happens when the PLC reconnects after you restart the broker.