News:

  • November 23, 2026, 07:05:40 AM

Login with username, password and session length

Author Topic: setting an alarm  (Read 13204 times)

maciek

  • Sr. Member
  • ****
  • Posts: 95
setting an alarm
« on: April 14, 2019, 09:28:08 PM »
in a brx plc working with a pid  i am looking for an easy way to set an alarm if the PID_0.PV gets bigger than the
 PID_0.SP by some percentage like 5 or 10

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: setting an alarm
« Reply #1 on: April 15, 2019, 06:06:13 AM »
Calculate the deviation percentage to your SP PV units, then use ALDEV.

maciek

  • Sr. Member
  • ****
  • Posts: 95
Re: setting an alarm
« Reply #2 on: April 15, 2019, 08:27:45 PM »
i wish that the ALDEV would give me an option of deviation percentage not a number because the number for 400 deg would be way different than 1200 deg and if that is not an option any ideas on how the calculation would look.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: setting an alarm
« Reply #3 on: April 16, 2019, 08:50:05 AM »
Use a MATH instruction to calculate a variable deviation (Dev).  The percentage value should be between 0.0 and 100.0
MATH Dev "(PV * Percentage) / 100.0)"

Then use Dev as the Deviation Limit in your ALDEV:
ALDEV Input:PV Setpoint:SP DeviationLimit:Dev PosAlarm:AlarmA NegAlarm:AlarmB