News:

  • November 23, 2026, 11:58:31 AM

Login with username, password and session length

Author Topic: PID Auto Tune  (Read 6781 times)

pbw

  • Hero Member
  • *****
  • Posts: 127
PID Auto Tune
« on: October 09, 2018, 06:56:40 PM »
Is the Auto Tune code in Do-More Designer or on the Do-More CPU itself?

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: PID Auto Tune
« Reply #1 on: October 09, 2018, 09:10:09 PM »
Both, but mostly the PLC.  Designer sets up the Auto-Tune and monitors it, and puts the loop back out of auto-tune mode, but the actual work is being done by the PLC.

Garyhlucas

  • Hero Member
  • *****
  • Posts: 421
Re: PID Auto Tune
« Reply #2 on: October 12, 2018, 09:20:30 PM »
Does this imply that the program might be able to force an autotune to occur? Would be useful if changing a pump or punp impellor required a different tuning.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: PID Auto Tune
« Reply #3 on: October 12, 2018, 11:20:19 PM »
Does this imply that the program might be able to force an autotune to occur? Would be useful if changing a pump or punp impellor required a different tuning.

Yes.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO