News:

  • November 26, 2026, 02:54:44 PM

Login with username, password and session length

Author Topic: completely new to plcs  (Read 84762 times)

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: completely new to plcs
« Reply #30 on: May 06, 2009, 11:15:40 AM »
Here's a non-stage version if you prefer.  I like to do the power up-handler as a subroutine (SBR) at the end of the program so you can ignore it during normal review.  I wanted to only set the pump bits and the alarm output once every second or so to avoid chattering the outputs, and would have done so inline, skipping it with a GOTO and LBL but the 05 doesn't support it, so that's in an SBR as well.  I also added the pump permissive input you mentioned.


PLC 05

// Rung 1
// Address 0
STR X0
OUT Y0

// Rung 2
// Address 2
STR X0
AND X1
OUT Y1

// Rung 3
// Address 5
STR SP4
OUT C0

// Rung 4
// Address 7
STRPD C0
GTS K2

// Rung 5
// Address 10
END

// Rung 6
// Address 11
SBR K1

// Rung 7
// Address 13
ANLGIN K0 K0 K2 K0 V200

// Rung 8
// Address 51
STR SP1
LD K1000
OUT V210
LD K3000
OUT V211
LD K4000
OUT V212
LD K200
OUT V213

// Rung 9
// Address 60
RT

// Rung 10
// Address 61
SBR K2

// Rung 11
// Address 63
STR V200 V210
ANDN V200 V211
OUT Y2

// Rung 12
// Address 68
STR V200 V211
ANDN V200 V212
OUT Y3

// Rung 13
// Address 73
STR V200 V212
OUT Y4

// Rung 14
// Address 76
STRN V201 V213
OUT Y5

// Rung 15
// Address 79
RT

// Rung 16
// Address 80
NOP


#BEGIN ELEMENT_DOC
"X0","On/Off switch","",""
"X1","Pump_Permissive","",""
"Y0","""System On""","","Indicator Light"
"Y1","Pump On","",""
"Y2","Fan speed 1","",""
"Y3","Fan Speed 2","",""
"Y4","Fan Speed 3","",""
"Y5","Alarm Output","",""
"V200","Channel 1","","Analog input"
"V201","Channel 2","","Analog input"
"V210","S.P. 1","",""
"V211","S.P. 2","",""
"V212","S.P. 3","",""
"V213","S.P. 4","","Low Pressure"

#END
« Last Edit: May 06, 2009, 01:27:13 PM by Controls Guy »
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

milldrone

  • Full Member
  • ***
  • Posts: 48
  • I'm changing my attitude to thumbs up
Re: completely new to plcs
« Reply #31 on: May 06, 2009, 07:11:11 PM »
imemotor, and Controlsguy

I took the liberty of adding some rung comments to Controlsguy's code (I hope he doesn't mind)

Now you can see some different styles of programming Controlsguy Vs. PLCnut.

Questions?

PLC 05

// Rung 1
// Address 0
STR X0
OUT Y0

// Rung 2
// Address 2
STR X0
AND X1
OUT Y1

// Rung 3
// Address 5
#BEGIN COMMENT
"This rung sends the PLC scan to the subroutine every half second"
""
"The next bit of text is a quote from Controlsguy"
""
"Quote:"
"""I wanted to only set the pump bits and the alarm output once every second or so to "
"avoid chattering the outputs, and would have done so inline, skipping it with a GOTO and "
"LBL but the 05 doesn't support it, so that's in an SBR as well."""
#END
STR SP4
GTS K2

// Rung 4
// Address 8
END

// Rung 5
// Address 9
#BEGIN COMMENT
"imemotor,"
""
"This is a subroutine because it's after the ""end"" statement it is scanned only one time"
""
"This section that Controlsguy has written only gets scanned during the first PLC scan after "
"a powerup or a PLC transition from stop to run. "
""
"On larger programs this kind of programming can make the PLC much faster."
""
"He has placed some values for setpoints here also like LD k1000 then do you see the "
"""out"" underneath? this is one of your setpoints to compare against."
""
""
""
#END
SBR K1

// Rung 6
// Address 11
ANLGIN K0 K0 K2 K0 V200

// Rung 7
// Address 49
#BEGIN COMMENT
"The values in this rung are just a guess. You have not given us any info on your "
"temperature probe & transmitter and your pressure sensor and transmitter. So that we can "
"help you scale them."
""
"You can also write to the PLC from the HMI to these setpoints the PLC will overwrite them "
"on powerup or a stop to run transition."
""
"So in you HMI if you wite a value to ""V210"" this will be your new setpoint"
#END
STR SP1
LD K1000
OUT V210
LD K3000
OUT V211
LD K4000
OUT V212
LD K200
OUT V213

// Rung 8
// Address 58
RT

// Rung 9
// Address 59
#BEGIN COMMENT
"The next bit of text is a quote from Controlsguy"
""
"Quote:"
"""I wanted to only set the pump bits and the alarm output once every second or so to "
"avoid chattering the outputs, and would have done so inline, skipping it with a GOTO and "
"LBL but the 05 doesn't support it, so that's in an SBR as well."""
#END
SBR K2

// Rung 10
// Address 61
#BEGIN COMMENT
"I still think you need to check your VFD manual out for info on preset speeds."
""
"These are normally done in a binary matrix"
""
"Fan speed 1out          Fan speed 2out        Fan speed 3out                VFD preset speed #"
"ON                               off                             off                                   = preset 1"
"off                               ON                            off                                    = preset 2"
"ON                             ON                             off                                    = preset 3"
"off                              off                               ON                                  = preset 4"
"ON                             off                               ON                                  = preset 5"
"off                              ON                              ON                                  = preset 6"
"ON                            ON                                ON                                = preset 7"
""
#END
STR V200 V210
ANDN V200 V211
OUT Y2

// Rung 11
// Address 66
STR V200 V211
ANDN V200 V212
OUT Y3

// Rung 12
// Address 71
STR V200 V212
OUT Y4

// Rung 13
// Address 74
STRN V201 V213
OUT Y5

// Rung 14
// Address 77
RT

// Rung 15
// Address 78
NOP


#BEGIN ELEMENT_DOC
"X0","On/Off switch","",""
"X1","Pump_Permissive","",""
"Y0","""System On""","","Indicator Light"
"Y1","Pump On","",""
"Y2","Fan speed 1","",""
"Y3","Fan Speed 2","",""
"Y4","Fan Speed 3","",""
"Y5","Alarm Output","",""
"V200","Channel 1","","Analog input"
"V201","Channel 2","","Analog input"
"V210","S.P. 1","",""
"V211","S.P. 2","",""
"V212","S.P. 3","",""
"V213","S.P. 4","","Low Pressure"

#END

Vaughn

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: completely new to plcs
« Reply #32 on: May 06, 2009, 09:50:20 PM »
Mind?  Why would I mind?  I got to do the fun part!   :D

One thing though.  I originally did STR SP4 GTS K2, but I think the internal clock bits are on a 50% duty cycle, so SP4 will be on for 0.5 sec, and off for 0.5 sec.  I meant to do a differential but forgot.  When I noticed I had posted a normal STR, I was going to go back and correct it, but then I noticed you can't do differential contacts on SP bits  (what the heck?), so I changed it to:

STR SP4 OUT C0

STRPD C0 GTS K2

and counted myself fortunate I got it changed real quick before Imemotor saw it!  So the version you commented is slightly obsolete.  Sorry about that!
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: completely new to plcs
« Reply #33 on: May 06, 2009, 10:35:02 PM »
PD coil with C0 parm would work.  What's good about having a differential function as a coil (in addition to contact) is that it is power-flow based, so you could have any combinational logic driving the PD.

If only there was a ONESHOT contact like the old TISOFT had in TI Series 500, then you wouldn't even need to burn a CR.

(cloud of logic)---] powerflow oneshot contact [------(GTS) (or MATH or whatever)

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: completely new to plcs
« Reply #34 on: May 06, 2009, 10:44:13 PM »
PD coil with C0 parm would work.

Equivalent to what I did.  Two rungs with four ops either way.

Quote
What's good about having a differential function as a coil (in addition to contact) is that it is power-flow based, so you could have any combinational logic driving the PD.

The differential coils don't enable that.  Since you guys have the nice STRPD's and STRND's, you can still do the combinatorial logic with a regular out coil, then apply the PD or ND to the contacts of THAT coil.  Plus this allows BOTH PD and ND, without having to commit to one or the other.

Now that I think about it, I guess the unique advantage of OUTPD and OUTND occurs when you use them with a NC contact.  If you do:

[logic]  OUTPD C0

STRN C0  [something enabled]

you get the stuff enabled every scan EXCEPT the first scan [logic] is true, which is hard to do with OUT/STRPD.  If that's the only contact on the second rung, you could do OUT/STRPD/NOT, but not if you want to use it in more complex logic.  So OUTPD does distinguish itself!  Plus (though I can't imagine why you would ever do this) you can do

[logic] OUTPD C0

STRND C0 [stuff enabled]  and get only the second scan!  Talk about arcana.

Quote
If only there was a ONESHOT contact like the old TISOFT had in TI Series 500, then you wouldn't even need to burn a CR.  (cloud of logic)---] powerflow oneshot contact [------(GTS) (or MATH or whatever)

I know, those were great!  I was having a discussion about that very topic with somebody a few months ago.
« Last Edit: May 07, 2009, 09:35:52 AM by Controls Guy »
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: completely new to plcs
« Reply #35 on: May 07, 2009, 09:52:08 AM »
Just remember the limitation of STRPD and STRND when working with a bit location which is affected by the ladder logic (C or Y for example). The instructions only function as expected AFTER the last OUT, SET, RST or whatever in that scan. The instructions do not wrap around to work BEFORE these rungs on the next scan.
An output is a PLC's way of getting its inputs to change.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: completely new to plcs
« Reply #36 on: May 07, 2009, 10:06:46 AM »
Are you serious?  I'm working on an AD PLC today and I'll have to check that out.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

imemotor

  • Newbie
  • *
  • Posts: 6
Re: completely new to plcs
« Reply #37 on: May 07, 2009, 10:21:01 AM »
Gentlemen,

Thanks for your help, you have given me a great jump start to programming.  Actually the only problem I am having now is to get the PLC to acknowledge my analog sensors.  Seems like it should be easy but I can’t get it to work.
 Analog card F0-04AD-1
Temperature transmitter TTD25N-20-0300F-H
Pressure Transmitter PTD25-20-0100H
My PLC is D0-05AR

I have figured out that the + - sensor leads don’t just plug into the analog card + - channel slots, apparently you need a separate 30V DC power source.  My PLC is AC with no DC power supply, so I have a separate DC power source running through the analog sensors back to the channel inputs on the analog card but is still doesn’t work.

I’m thinking maybe my sensors need to run through a step down resistor?

IMEMOTOR

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: completely new to plcs
« Reply #38 on: May 07, 2009, 10:25:22 AM »
Here's a thread on the STRPD/STRND limitation from the AD forum: http://forum.automationdirect.com/showthread.php?t=1476&highlight=strpd

 Look for the PDF tech reference in post #16

I also talk about it on my site: http://www.theplcguy.com/ABtoAD/Differential.html
An output is a PLC's way of getting its inputs to change.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: completely new to plcs
« Reply #39 on: May 07, 2009, 10:40:31 AM »
Gentlemen,

Thanks for your help, you have given me a great jump start to programming.  Actually the only problem I am having now is to get the PLC to acknowledge my analog sensors.  Seems like it should be easy but I can’t get it to work.
 Analog card F0-04AD-1
Temperature transmitter TTD25N-20-0300F-H
Pressure Transmitter PTD25-20-0100H
My PLC is D0-05AR

I have figured out that the + - sensor leads don’t just plug into the analog card + - channel slots, apparently you need a separate 30V DC power source.  My PLC is AC with no DC power supply, so I have a separate DC power source running through the analog sensors back to the channel inputs on the analog card but is still doesn’t work.

I’m thinking maybe my sensors need to run through a step down resistor?

IMEMOTOR


Refer to http://web1.automationdirect.com/static/specs/f004ad1.pdf for wiring.  The "+" shown in that diagram at the transmitter is Pin 1 on your temp transmitter (brown if using AD cable) and the "-" is Pin 2 (white).  The pressure transducer is probably similar.  So DC+ to transmitter brown, transmitter white to PLC CH1+, CH1- to DC -, and also ground the DC-.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.