News:

  • October 24, 2026, 01:15:32 PM

Login with username, password and session length

Author Topic: BX-DM1E-18ED23 lost IP adddress.  (Read 7822 times)

Tam1117

  • Jr. Member
  • **
  • Posts: 13
BX-DM1E-18ED23 lost IP adddress.
« on: March 28, 2018, 08:28:41 AM »
Hi all,

I have 1 C-More and 6 BX-DM1E-18ED23's on Ethernet. Today I just turned power on and
the C-more messages: PLC communication timeout.
Two of the 6 PLC's IP address go back to default!
I know that the IP address is stored in the ROM, so what should we do to prevent this?
Using SETUPIP with $FirstScan?

Thanks.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BX-DM1E-18ED23 lost IP adddress.
« Reply #1 on: March 28, 2018, 09:59:05 AM »
The IP settings are stored in the same flash memory as the GA, OS, user program, system config, etc, so it is highly unlikely that they just 'lost' the settings without affecting anything else.

You mentioned powering up the PLCs. Did you recently clear them PLC memory and reload them? If the System Settings were cleared when you did that, the Ethernet ports will continue to work until the PLC is power cycled.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Tam1117

  • Jr. Member
  • **
  • Posts: 13
Re: BX-DM1E-18ED23 lost IP adddress.
« Reply #2 on: March 29, 2018, 01:36:22 PM »
Yes, you were right, thank.