News:

  • October 23, 2026, 05:59:24 PM

Login with username, password and session length

Author Topic: PID View  (Read 6725 times)

Evilbeard

  • Hero Member
  • *****
  • Posts: 160
PID View
« on: February 16, 2018, 09:12:16 AM »
Is there currently a way to scale the output window in the PID view? I'm using an output of 0-100%, and I'd like to be able to look at it visually with a little more resolution, but I have to waste half the the chart that I'm not using.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3853
    • Host Engineering
Re: PID View
« Reply #1 on: February 16, 2018, 10:29:15 AM »
Inside the PID view itself, no.

However, you could create a generic Trend View with just the MyPID.Output value in 1 pane, and Trend View has more options since it is just a generic Trend View, one of which is manually scaling the Y axis - after thinking about it, actually, even the Auto Scaling in Trend View will probably give you the resolution you want/need.