I have application to solve and I was thinking you are address to ask.
I need to monitor temperature in 32 points in meat storage space.
Monitoring will be in one room on PC and data should  be saved at list 15 days.
I would like to use Automation Direct product.
My question is what is easyest and economical way to solve this problem.
If somebody gave me quiq instruction you will oblige me.
Thank you.
Dejan,NS, Srbija
« Last Edit: April 13, 2007, 11:10:40 PM by BobO »

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Temp monitor application
« Reply #1 on: April 10, 2007, 04:12:09 PM »
The family of hardware components that gives you fewest number of modules required to read 32 temperatures is the Terminator I/O family, using the T1F-16RTD. This modules has 16 RTD inputs, you'll need two of them to get your required 32 temperature inputs. You'll need one T1K-01AC power supply.

You also need either a T1H-EBC or T1H-EBC100 network interface module. You choice will depend on what communication protocol the PC software will be using to read the data. The main difference between these interface modules is the T1H-EBC100 supports everything the T1H-EBC does, and adds Modbus/TCP protocol support.

--MikeS