Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: Telemecanique Schneider MODBUS
« Reply #15 on: June 30, 2016, 07:51:12 PM »
Except for this from the ATS48 Modbus Manual:

Quote
Representation of data
The ATV48 parameters are 16-bit words designated by "W…" (…address in decimal notation).
They are used to represent unsigned values (0 to 65535), ie. 16 independent logic states.
In this case, they are called "registers", and the notation for their bits is "W…:xk" (k bit number, from 0 to 15).


Yes the manual does say ATV48 here but it is from the ATS48 Modbus Protocol manual.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: Telemecanique Schneider MODBUS
« Reply #16 on: July 01, 2016, 06:32:36 AM »
I guess I only thought that I tried +1. 4063 got me where I needed to be.
Sorry for running everyone around over nothing. Thanks for your help.