I was getting a weird error yesterday after installing an additional remote rack, updating firmware in the PLC H2-DM1E to the latest and loading in the program changed offline. It was ST136 $IOMapError but I could not figure out why, only that it was the new rack - 6 slot with EBC-100, F2-8AD4DA-2 and D2-08CDR. The solution turned out to be increasing the WX and WY memory sizes. I don't recall how much I went up, maybe 320 so 0-319 each. But I don't understand why 308 elements each (for WX0-307 and WY0-307) was giving an error when WX307 and WY306 are the last addressed.
Yes manual addressing and also yes, I forgot about right clicking the bar to set the starts.