News:

  • November 25, 2026, 04:55:48 PM

Login with username, password and session length

Author Topic: Invalid instruction after firmware upgrade  (Read 10891 times)

amezcackle

  • Newbie
  • *
  • Posts: 9
Invalid instruction after firmware upgrade
« on: December 12, 2015, 01:56:26 PM »
After updating a Do-More to these versions:

OS 1.4.1
Booter 3.06
FPGA 3.6
Hardware 7B

and performing a power cycle, I get an error message when attempting to load a program with a WX instruction.

These are the errors:

S233, Fri Dec 11 14:57:05 2015, System content changed by Administrator (Program)
S234, Fri Dec 11 14:57:05 2015, Invalid instruction 0xBD000013 at 781.
S235, Fri Dec 11 14:57:05 2015, Program validation failed! Reverted to old program

The program check by Designer is OK. Is this possibly a CPU failure? I haven't tried a new CPU yet. Any Ideas?

Mike

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Invalid instruction after firmware upgrade
« Reply #1 on: December 12, 2015, 04:10:48 PM »
Yuk. This is typically the result of a firmware/DmD version mismatch, but that seems correct. Please make sure that all DIP switches are off, and try again. If it still fails we might have an encoding/validation hole.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

amezcackle

  • Newbie
  • *
  • Posts: 9
Re: Invalid instruction after firmware upgrade
« Reply #2 on: December 14, 2015, 01:38:37 PM »
I just swapped out the CPU and all is working as it should. I assume a faulty CPU, possible lightening damage.
Thanks
Mike

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: Invalid instruction after firmware upgrade
« Reply #3 on: December 15, 2015, 01:55:38 PM »
I sent you a PM about this CPU.
Good design costs a lot. Bad design costs even more.

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: Invalid instruction after firmware upgrade
« Reply #4 on: February 12, 2016, 10:06:42 AM »
I sent you another PM this morning.
Good design costs a lot. Bad design costs even more.