News:

  • November 27, 2026, 03:51:02 AM

Login with username, password and session length

Author Topic: T1H-DM1 unable to attach my computer  (Read 18499 times)

rickshea1

  • Jr. Member
  • **
  • Posts: 18
T1H-DM1 unable to attach my computer
« on: May 21, 2015, 04:49:04 PM »
Hello

I have a T1H-DM1 SN:00 00 1C 00 00 67 and it has a problem somewhere. There are times when I go to attach to the CPU and my computer says "unknown device" and you can not attach to it. You have to power down / up the system and maybe it will attach to the computer. It always attach's after a third attempt. Today I noticed the operator interface could not change modes. That's very odd since it's worked all day. When I went to attach I got the "unknown device" again. After cycling the power again I could attach and the operator interface worked. Is there a problem with the early Do Mores. It only seems to be this CPU.
OS = 1.3.2
Booter = 1.0.2
FPGA = 1.2
Hardware = 3a

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: T1H-DM1 unable to attach my computer
« Reply #1 on: May 21, 2015, 08:04:10 PM »
Since your Operator Interface is also having issues, you might want to check your grounding.  What you are describing is a pretty common issue when there is a poor ground connection to the PLC.  Measure Neutral to Ground, the voltage should be less than 0.1VAC.

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: T1H-DM1 unable to attach my computer
« Reply #2 on: May 22, 2015, 07:39:19 AM »
Thank you. I'll check that out this morning.

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: T1H-DM1 unable to attach my computer
« Reply #3 on: May 22, 2015, 09:00:19 AM »
Here is an update on the "Neutral to Ground" voltage. On the AC side I didn't see any or the tester I used couldn't pick any up. Most of our systems are DC including the racks or power supplies so as a test I checked the 0vdc and ground. there was a difference of 0.14 - 0.18 volts. I grounded out the 0vdc line and now read nothing. I will continue to attach and detach my computer for the next couple of days and see if that helped with the CPU comm ports and the interface communications.

Thanks  
« Last Edit: May 22, 2015, 09:02:34 AM by rickshea1 »

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: T1H-DM1 unable to attach my computer
« Reply #4 on: May 22, 2015, 09:25:19 AM »
DC supplies are frequently troublesome with serial comm ports and it seems like it is always grounding issues.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: T1H-DM1 unable to attach my computer
« Reply #5 on: May 22, 2015, 12:03:41 PM »
Well it's not the power supply or the grounding. I just tried to attach to the CPU (T1H-DM1) and this is what I got. "USB DEVISE NOT RECOGNIZED. One of the USB devices attached to this computer has malfunctioned and windows does not recognize it.". This time I tried to reboot my computer and see what happens. Same response. I cycle the power on the CPU and it works. Something in the CPU is being jazzed up and it takes a reboot to fix it? any ideas. This machine is shipping out to California soon. When I talk to Automation Direct they say they have never heard of this happening. Anyone know how I can get a hold of HOST directly? I've already tried to reload the drivers. Twice. Same thing.
« Last Edit: May 22, 2015, 12:06:54 PM by rickshea1 »

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: T1H-DM1 unable to attach my computer
« Reply #6 on: May 22, 2015, 03:40:04 PM »
Do-more Designer does not ship and USB drivers for communication with the do-more CPU, it uses a driver that is shipped with the Windows OS. So which drivers are you trying to reload ?

Let me make sure I understand the hardware setup you have:

the terminator power supply you are using is the a T1K-01DC ? and is the DC power coming from a transformer ? or a generator ?

Is the computer running Do-more Designer a laptop ? if so, does it help if you run the laptop off of it's battery ?

Are there other comm devices plugged into the T1H-DM1E cpu ? do they get power from a different source ?

Good design costs a lot. Bad design costs even more.

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: T1H-DM1 unable to attach my computer
« Reply #7 on: May 22, 2015, 04:32:31 PM »
Hello

Yes the terminators power supply is DC and the power is coming from a transformer with a line conditioner. The computer is a lap top and I've run it both ways with AC and with the battery. I will get the same response. There is an operator interface attached and it shares the same power supply as the PLC's power supply.

It's been awhile I believe I did a windows driver re-install and I've re-installed the Do more software at least once maybe a month ago on the advise of Automation Direct. Note: the software is up to date. The odd thing is this is the only CPU I have trouble with. What throws me is that I can attach - detach and it's good or when I go to attach again I might get this fault. It only goes away when I power down and up the CPU. The fault will go away. I wouldn't be so concerned if it wasn't for the fact the interface couldn't make a change until I recycle the CPU. It did not loose communications it just could change anything. I am in "term" mode.

Rick   

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: T1H-DM1 unable to attach my computer
« Reply #8 on: May 23, 2015, 08:30:10 AM »
Today and Tuesday I'm going to continue to attach and detach using my personal computer. This should narrow down the "USB DEVISE NOT RECOGNIZED" problem.

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: T1H-DM1 unable to attach my computer
« Reply #9 on: May 27, 2015, 08:35:22 AM »
I switched computers for two days (I used my personal computer) to attach and It did not fail. I then looked at the drivers in my programming computer and found a "USB Virtual Driver" listed among the drivers. My personal computer did not have that driver so I deleted it from my programming computer. I tried to attach my programming computer to the CPU this morning 6 times using different ports and It did not fail. Unfortunately we had to start to break it down for shipping. Perhaps that "USB Virtual Driver" was causing a problem. Thanks for all your help.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: T1H-DM1 unable to attach my computer
« Reply #10 on: May 27, 2015, 10:48:38 AM »
Entirely possible. There are other examples (looking at you, Dell Stage) of applications that mess us up on USB.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: T1H-DM1 unable to attach my computer
« Reply #11 on: May 27, 2015, 12:50:15 PM »
"USB Virtual Driver" is generally used for Virtual Machines such as the XP virtual machine that can be installed in Windows 7.  It is basically a way to redirect a USB driver to another operating system than the main one that boots.  It certainly can cause the issues that you were describing.