« on: May 05, 2015, 11:43:03 AM »
We have about 7 Terminator Do Mores in the field. All work well but one (1). The CPU will turn itself "OFF" and than back "ON" maybe twice in 8 hours for no reason. We've check all the wiring and all the wiring is good. We use the Terminator 24 vdc power unit only to supply the CPU. We use a separate P.S. for the rest of the I/O. We've replaced the CPU but have the same results. Two of my thoughts are 1. replace the power supply. 2. This company has two (2) or three (3) rather large transformers with-in 4 feet of our machine could this cause a problem?

Has anybody else had a problem like this?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: PLC turning itself OFF aand back ON
« Reply #1 on: May 05, 2015, 11:48:59 AM »
What is the value in DST385 ($WatchdogReboots)?
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: PLC turning itself OFF aand back ON
« Reply #2 on: May 05, 2015, 11:56:05 AM »
I have no idea. I've never looked at that register. I have a man in the field updating is computer software so he can attach. I'll have him look. Whats the importance or what should I be looking for?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: PLC turning itself OFF aand back ON
« Reply #3 on: May 05, 2015, 12:00:30 PM »
When a DM1x CPU reboots itself due to a watchdog timeout, it sets $WatchdogReboot (ST13) and increments $WatchdogReboots (DST385). If it is crashing and restarting, it is likely due to noise. If the watchdog counter is not incrementing, it is likely a failure in the power supply (which could be noise, unstable power, or bad power supply).
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

rickshea1

  • Jr. Member
  • **
  • Posts: 18
Re: PLC turning itself OFF aand back ON
« Reply #4 on: May 05, 2015, 12:04:25 PM »
That's great information. I'll have to get back to you. It could take some time before my man gets back to me.