News:

  • November 27, 2026, 12:54:21 AM

Login with username, password and session length

Author Topic: Do more and 205 base  (Read 19460 times)

Henryp

  • Hero Member
  • *****
  • Posts: 161
Do more and 205 base
« on: April 07, 2015, 02:58:15 PM »
I would like to change out a 450 PLC to a Do-more but I'm one slot short of what I need.  If a 205 base had a larger power supply could a Do-More address more than a 9 slot base?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Do more and 205 base
« Reply #1 on: April 07, 2015, 03:39:43 PM »
Do-more can handle up to 16 slots in the local base, and Terminator does that, but the DL205 base design is limited to 8 modules.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: Do more and 205 base
« Reply #2 on: April 07, 2015, 06:31:37 PM »
A larger base for the Do-More would be nice.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Do more and 205 base
« Reply #3 on: April 07, 2015, 06:56:24 PM »
We understand. We're looking at options for increasing I/O capacity for Do-more.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: Do more and 205 base
« Reply #4 on: April 07, 2015, 08:49:32 PM »
I would like to change out a 450 PLC to a Do-more but I'm one slot short of what I need.  If a 205 base had a larger power supply could a Do-More address more than a 9 slot base?
205 Do-more can address thousands of I/O using Ethernet I/O.  The 450 PLC scan time is very slow compared to Do-more, even with Ethernet I/O.  Do you think you could use Ethernet I/O expansion bases (up to 16 slaves)?

Or, are you looking for higher density I/O due to foot-print concerns?  I know that the Terminator I/O has some higher density analog and discrete.  You could even use this high density Terminator I/O for your Ethernet I/O expansion bases with your 205 local base, if you need the density.  Or just have all Terminator I/O with your Terminator T1H-DM1E CPU in the local base and T1H-EBC100 CPU in the expansion bases.
« Last Edit: April 07, 2015, 08:52:27 PM by franji1 »

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: Do more and 205 base
« Reply #5 on: April 15, 2015, 11:29:29 AM »
I could use Ethernet I/O.  It turns out I was able to split the 450 into two PLCs. A Do-More is doing all of the control work and a 250 is collecting a few analogs signals. This is the last 450 at my plant. The conversion utility worked well. 

Thanks for a great CPU!

plcnut

  • Hero Member
  • *****
  • Posts: 816
    • premiersi.com
Re: Do more and 205 base
« Reply #6 on: April 15, 2015, 11:49:06 AM »
.... A 205 base with a cpu slot and 16 module slots .... :drool: ...that would look so nice in a cabinet...
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
https://premiersi.com

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Do more and 205 base
« Reply #7 on: April 15, 2015, 12:26:05 PM »
I don't think I'd personally like using a 16-slot 250.  It'd be 4" high x 2' long.  If I have that much I/O in one rack, I'd rather see a taller, higher I/O count per module option about the size of the 405 or AB SLC.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: Do more and 205 base
« Reply #8 on: April 15, 2015, 06:45:35 PM »
There would appear to be a D2-64TD1 being sold somewhere in the world (as well as a D2-265.) I could have used that 64 pt DC In last year. The 265 would have been nice before the Do-more came along. It might still be every now and again, but I wonder if the cost wouldn't be excessive in comparison to the H2-DM1E?

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: Do more and 205 base
« Reply #9 on: April 15, 2015, 08:27:11 PM »
I really like Do-more.   ;)

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Do more and 205 base
« Reply #10 on: April 15, 2015, 08:58:58 PM »
64 point modules couldn't pass UL due to temp rise.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO