This contains the last 4 reboot states and the current state.
518 = normal operation following a program update
806 = normal operation following a transition to run mode
413 = normal operation following a boot to program
801 = failed running user logic during the first scan
The top three are normal and expected. When you make a program change, you'll see 518. When you switch to run mode, you'll see 806. When you power up in program mode, you'll see 413.
The 801 is where the problem occurred. It failed during a transition to run mode, while running user logic the first time.
What I/O modules do you have in each slot?
What module configs do you have listed?