You have the "Off by one register plus wrong word order" issue you can get with floats
24.2456 -> 253,246,193,65 (byte values)
24.125 -> 0,0,193,65
981.2389 -> 74,79,117,68
983.8592 -> 253,246,117,68
(Note bytes 253 and 246 that are actually part of the first value are being interpreted as part of the second)
You'll definitely have to change word order on one end or the other. Lookout is probably easier.
You won't be able to write to MHR0, and I don't think Do-More is going to let you cast 1&2 as a double because of alignment, so in addition to fixing the word order you're probably going to need to change Lookout to 2&4 and stop trying to use either 0 or 1 as part of a 32-bit write.