News:

  • June 26, 2026, 07:54:36 PM

Login with username, password and session length

Author Topic: Trying to control air cylinder  (Read 9743 times)

timk

  • Jr. Member
  • **
  • Posts: 15
Trying to control air cylinder
« on: September 27, 2014, 11:25:20 AM »
Need some help with ladder to control an air cylinder with sensors.

I have a 10" air cylinder with 2 sensors one spaced 3" from each end
I have a counter that is triggered from another sensor When the counter reaches 2 I want the cylinder to come on until the first sensor is on and stop there. When the counter reaches 3 It needs to come on again until it reaches the second sensor. and at a count of 4 it needs to come on and stay on.

I have tried
CT1.ACC=2 --- [/X6] ---- [Y16]  "X6 is the first sensor on the cylinder Y16 is the air valve

CT1.ACC=3 --- [/X7] ---- [Y16]  "X7 is the Second sensor on the cylinder

CT1.ACC=2 --- [/X6] ---- [Y16 Delay Off 3 Seconds]  "Now I just want the air valve to come on and stay on for a few seconds.

But when I try to run it [Y16] never come on even though the CT1.ACC is 2 and [X6] is on. (Status on both is green) but the output is never on.




b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: Trying to control air cylinder
« Reply #1 on: September 27, 2014, 12:31:31 PM »
You should only have the output once in the ladder. Otherwise the state of the last rung controls the output.

Here are two ways to modify your logic:

Combine each of your conditions as parallel segments then end in just one output.

Keep your separate conditions but end each with a unique 'C' bit. Then add a final rung with each of these 'C' bits in parallel driving one output. This is probably the more 'readable' form as you can concentrate on each condition separately.
An output is a PLC's way of getting its inputs to change.

timk

  • Jr. Member
  • **
  • Posts: 15
Re: Trying to control air cylinder
« Reply #2 on: September 27, 2014, 12:42:09 PM »
Thanks, That makes sense

Now it looks like a need to find a 4 or 5 way air valve. The one they got me to use has 2 coils but Port A or B is always on.


plcnut

  • Hero Member
  • *****
  • Posts: 814
    • premiersi.com
Re: Trying to control air cylinder
« Reply #3 on: September 29, 2014, 08:18:58 AM »
Sounds like you need a 4-way Closed center valve.
But do be aware, that positioning with a standard pneumatic valve/cylinder at any position other than end of stroke is very finicky, and is generally un-reliable and non-repeatable especially with varying loads... it all depends on your application.
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
http://premiersi.com

timk

  • Jr. Member
  • **
  • Posts: 15
Re: Trying to control air cylinder
« Reply #4 on: October 03, 2014, 11:19:45 AM »
Thanks

I am not really looking for precision or repeat-ability it is only to help test an addition to a machine we are designing. The finished product will more than likely use a servo or something. I was hoping I could just restrict the exhaust on the down stroke, apply air for a few ms each time I needed the cylinder to move down. But it only worked once in a while.(almost never)

So I added a couple of proxes to mid points on the cylinder. But cant seem to get the ladder sequence correct. I assume the only way to do it would be to have a valve move the cylinder down until the first prox makes. Then if the first prox goes off turn on the up valve until first prox makes again.
 
Does anyone have a ladder example of controlling the position of an air cylinder they would be willing to share.