Can I address PID structure fields directly or do I need to move date into and out of them first?  For example I need to send a setpoint from a RedLion G3 HMI but the Do-More driver it has doesn't drill down that far in memory types. So what I have been doing is sending the SP to R0 and the moving it into .SP

I thought I had a light bulb moment when I thought to import the tag database into the RedLion but the PID fields don't seem to export from Do-More.


BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6161
  • Yes Pinky, Do-more will control the world!
Re: PID Structure Field addressing
« Reply #1 on: August 28, 2014, 09:03:51 PM »
Everything is publicly accessible, the limitations are in the driver, so I don't have an immediate answer. You might try creating a nickname for YourPID.SP and exporting that.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

rlp122

  • Sr. Member
  • ****
  • Posts: 91
Re: PID Structure Field addressing
« Reply #2 on: August 29, 2014, 08:33:09 AM »
I don't think Red Lion implemented internal structures, IIRC.  You'll need to move it in and out.

HABCO

  • Newbie
  • *
  • Posts: 2
Re: PID Structure Field addressing
« Reply #3 on: August 29, 2014, 08:43:08 AM »
Thanks Everyone!