News:

  • September 04, 2026, 05:00:22 AM

Login with username, password and session length

Author Topic: Do-More ethernet for multiple racks and data logging  (Read 7284 times)

davidbgtx

  • Hero Member
  • *****
  • Posts: 215
  • Host be the Most
Do-More ethernet for multiple racks and data logging
« on: August 12, 2014, 08:01:46 AM »
Can/could you use the ethernet port as expansion (say a couple of drives as Modbus/TCP, 2 racks with the H2-ECOM, 1 rack with T1H-EBC100, a C-More touchscreen) and also send data to Kepware over the same Port.

 I have a setup now with WinPLC, an ERM, 2 GS-EDRV's, TIH-EBC100 rack, a C-More touchscreen, 2 racks with H2-EBC100, and logging to kepware over same ethernet using a hub. There is a H2-CTRIO in one of the EBC racks. This config has been working for quite some time, but is very slow, looking for a way to speed things up and thought maybe the Do-More would be the ticket. What do you think?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6175
  • Yes Pinky, Do-more will control the world!
Re: Do-More ethernet for multiple racks and data logging
« Reply #1 on: August 12, 2014, 08:56:23 AM »
It should work fine. Obvious consideration is the more you do the more scan variation, but anything a WinPLC can do, Do-more should do better.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO