News:

  • November 26, 2026, 06:51:15 PM

Login with username, password and session length

Author Topic: M240 Common Modbus/TCP Client Device error  (Read 10246 times)

nfei

  • Jr. Member
  • **
  • Posts: 14
    • North Fork Electric Inc.
M240 Common Modbus/TCP Client Device error
« on: April 19, 2014, 12:23:11 PM »
I am using a DoMore talking to a MB_Gateway talking to multiple Modbus serial motor starters. I have one system working well. talking to 8 starters controlling them and monitoring % load. I am building another system and I cannot get it to work. I have copied my configuration from the running one and the MB-Gateway config. My writes work but I cannot read.
On the system that will not work I am getting "M240 Common Modbus/TCP Client Device... TCP overhead is minimized when one Do-More Modbus Client Device is created for each Modbus Server/Slave IP address. I do not get this message on the running system. I think I called in last year and a tech solved the problem for me, but I do not remember what it was. This may not be the cause of my read problem but it is a start.
MB-Gateway shows no errors in the status page.
Help?

nfei

  • Jr. Member
  • **
  • Posts: 14
    • North Fork Electric Inc.
Re: M240 Common Modbus/TCP Client Device error
« Reply #1 on: April 19, 2014, 01:08:44 PM »
I found the solution to the Common Modbus error; wrong IP address in one of my reads. It still has not fixed my read problem.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: M240 Common Modbus/TCP Client Device error
« Reply #2 on: April 19, 2014, 02:30:56 PM »
The message is just a gentle nudge to get you consider using one client device for each server. Much, much more efficient that way. Using a single client is like using 1 telephone to talk to 8 people: dial, talk, hang up...repeat 7 times. With 8 phones you dial each once, and leave the line connected. Much faster.

If you are talking to the gateway, however, you'll only need one client...which I think you've discovered.

As for your issue, I think we're going to need more info. Let's see...nfei...I know you, and you know us...so give us a call Monday and I'm sure we can get you running.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: M240 Common Modbus/TCP Client Device error
« Reply #3 on: May 08, 2014, 03:21:30 PM »
Modbus serial motor starter that is something we would like to do. Do you have a part number and any suggestions?

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: M240 Common Modbus/TCP Client Device error
« Reply #4 on: May 08, 2014, 06:29:24 PM »
Pretty sure that's a DL05 or dumb Modbus I/O brick sitting next to a starter. :D
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

nfei

  • Jr. Member
  • **
  • Posts: 14
    • North Fork Electric Inc.
Re: M240 Common Modbus/TCP Client Device error
« Reply #5 on: December 04, 2015, 11:48:09 AM »
Sorry, I just saw your request for info on the Modbus starters we are using. We are using the Schneider (Square D - old Telemechaniqe) U-Line series. They are DIN style starters in a wide range of sizes and both FV and FVR. They have an intelligent module for monitoring %load and other factors and you use a plug-in Modbus module for monitoring and control. Like all things SD, documentation is hard to find but the products are great; once you figure out how to use them! No picking up the phone and having an tech guy in <5min like AutomationDirect! This stuff is from France and a lot gets lost in translation!

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: M240 Common Modbus/TCP Client Device error
« Reply #6 on: December 04, 2015, 11:51:11 AM »
So, are you still having issues...after a 1.5 years? ;) We're still here if you need us...
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

nfei

  • Jr. Member
  • **
  • Posts: 14
    • North Fork Electric Inc.
Re: M240 Common Modbus/TCP Client Device error
« Reply #7 on: December 04, 2015, 12:07:05 PM »
Hi Bob, no we got it working very well. HenryP asked for the part numbers for the Modbus controlled starters we are using and I missed seeing it. Only took me 1 1/2 years to respond to him! It would be nice if AD would offer a Modbus controlled/monitored starter.
Hope you are well. What its been 15-20 years? Time flies! You guys are really doing a great job. I talk your praises to everyone that will listen, even ones that don't! Sure are a lot of bullheaded AB and GE addicts out there!