News:

  • October 14, 2026, 01:27:43 AM

Login with username, password and session length

Author Topic: d0-05DR and D0-08TR  (Read 43676 times)

theodejong87

  • Newbie
  • *
  • Posts: 2
d0-05DR and D0-08TR
« on: January 21, 2008, 07:32:11 AM »
Hello,

I have a D0-05DR witch I have to program with a D2-HPP handheld programmer. I have found out how to program the normal in and outputs but for the expansion D0-08TR 8 extra outputs but I can’t find out how to program these with the handheld programmer, I have tried to make them Y8 and but that was not the right way.

Is there anyone who can tell me how to program those outputs I would be ferry thankfully.
 
Thanks,
Theo

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: d0-05DR and D0-08TR
« Reply #1 on: January 21, 2008, 09:11:47 AM »
I believe that the 05, like the 06 with which I am more familiar, starts the I/O points of the add-on cards at X100 and Y100. Try that. You might want to read the manual also. It's available online.
An output is a PLC's way of getting its inputs to change.

theodejong87

  • Newbie
  • *
  • Posts: 2
Re: d0-05DR and D0-08TR
« Reply #2 on: January 22, 2008, 05:48:34 AM »
thank you ferry much, i have red the manuals wich are online. but i could not find the part where the add-on cards are discriped.
 but now I can co on with my school project.
thanks again.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: d0-05DR and D0-08TR
« Reply #3 on: January 22, 2008, 06:38:25 PM »
I too looked again at the online manuals. The first place I found the addressing of the add-on modules mentioned is on page 2-15 of the D0-OPTIONS-M manual.
An output is a PLC's way of getting its inputs to change.