News:

  • November 23, 2026, 01:16:35 PM

Login with username, password and session length

Author Topic: $Critical IO Error (ST148) How to trace cause?  (Read 11334 times)

ERokc

  • Hero Member
  • *****
  • Posts: 118
$Critical IO Error (ST148) How to trace cause?
« on: July 19, 2013, 08:41:38 PM »
I can Re-initialize IO and it clears but I would like to know which module is causing the error and why.
H2-DM1E, PLC is in RUN but nothing on the machine is moving and I get a audable DING on the PC and a red error at the Designer bottom screen.  PLC goes to PROGRAM and will not RUN until a power off or re-init then it will RUN.  This has happened three times during editing instruction in Designer.

Any way to tell who's got the problem?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: $Critical IO Error (ST148) How to trace cause?
« Reply #1 on: July 19, 2013, 11:18:20 PM »
Critical I/O errors are the result of a module not responding with the proper module ID during a normal input scan. Could be a flaky backplane, backplane connection, or module. The specific name alludes me...probably something like $LocalIOMaster...but there is a structure that contains a list of bit masks for each slot. Check the .Slots0_31 member to see which slot(s) are bad.

For DmD 1.1, we have added a very nice utility that displays all of this information automatically. It is much, much easier to use...and will be out shortly.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO