Do More and OPC communication
« on: June 06, 2013, 04:36:18 PM »
It appears that Kep Direct doesn't support the Do More PLC. What OPC server is typically used with the Do More?

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: Do More and OPC communication
« Reply #1 on: June 06, 2013, 05:33:44 PM »
It appears that Kep Direct doesn't support the Do More PLC. What OPC server is typically used with the Do More?
We recommend using Modbus (either Modbus/TCP or Modbus/RTU) - this would access the Modbus Server/Slave memory areas in a Do-more (i.e. NOT X/Y/C/V, but MI (Modbus (Discrete) Input), MC (Modbus Coil), MIR (Modbus Image Register), MHR (Modbus Holding Register)).

So, from a Modbus Master, you would want a field tied to reading Modbus Holding Register 40001.  The 4 is more of a "type", and 1 is the "offset".  So from Kep Direct's Modbus driver, Holding Register 40001 would access Do-more register MHR1 (not MHR40001), so write your Do-more PLC ladder logic to put the value for 40001 into MHR1.  If Kep Direct was reading Modbus Input Register 30001, it would address MIR1 (not MHR1) register in Do-more.

If you are familiar with the DirectLOGIC (DL) K-Sequence driver for KepDirect, you could use THAT driver (either Serial or Ethernet).  This DL implementation also uses similar "guest protocol" memory for reading X/Y/C/V, in that they will NOT access directly the Do-more X/Y/C/V data-blocks (for one, DL is OCTAL, Do-more X/Y/C/V are DECIMAL).  Use the DLX, DLY, DLC, and DLV data-blocks in Do-more (these are similar to the MI, MC, MHR, MIR for Modbus mentioned above).  So, in your Kep Server, if you wanted to read X10 (yes, octal 10), you would be reading DLX10 in a Do-more.  If you wrote to a K-Sequence tag tied to V2000, you would be writing to DLV2000 in the Do-more.

Unless you really like K-Sequence and octal, I recommend sticking with Modbus.

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: Do More and OPC communication
« Reply #2 on: July 03, 2013, 02:50:29 PM »
Kepdirect will not allow me to define static tags as a DL_ any data type (V,C,X or Y) and it t doesn't appear to have generic Modbus support. So how would I read 40001 and what devive type would I use since a DoMore processor is not a choice?
« Last Edit: July 03, 2013, 02:52:09 PM by Henryp »

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Do More and OPC communication
« Reply #3 on: July 03, 2013, 02:55:41 PM »
You don't enter it as DLX, just X. DLX is where it shows up in Do-more. Select DL260 as the CPU.

I believe ADC has an app note that spells this all out in detail.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: Do More and OPC communication
« Reply #4 on: July 03, 2013, 03:11:50 PM »
Here's the link to the App Note KEPDirect & Do-more:

http://support.automationdirect.com/docs/an-kep-005.pdf