Do More thermocouple
« on: April 22, 2013, 11:51:32 PM »
Hello All,

Can anyone point me in the right direction with a F2-04THM.
I have a thermocouple connected to CH1, but WX0 is reading 0.

The manual doesn't cover domore plc's.

Thanks
Rastus

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3806
    • Host Engineering
Re: Do More thermocouple
« Reply #1 on: April 23, 2013, 01:07:10 AM »
See if there are any details you need in the Do-more manual

Here's the link to chapter 6:
http://www.automationdirect.com/static/manuals/h2dmm/ch6.pdf

and a link to a page containing links to all the chapters:
http://www.automationdirect.com/pn/doc/manual/h2-dm1e

Rastus81

  • Jr. Member
  • **
  • Posts: 15
Re: Do More thermocouple
« Reply #2 on: April 23, 2013, 01:14:19 AM »
Thanks,

I have that manual. But it only outlines the jumper settings. Im wondering if i need to use any instructions to read the data, like they outline in the module manual.
http://www.automationdirect.com/static/manuals/d2anlg/ch7.pdf


franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3806
    • Host Engineering
Re: Do More thermocouple
« Reply #3 on: April 23, 2013, 09:08:13 AM »
I'm not a thermo-couple person, so I don't know how/if the wiring can cause what you are seeing.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6154
  • Yes Pinky, Do-more will control the world!
Re: Do More thermocouple
« Reply #4 on: April 23, 2013, 09:14:59 AM »
The short answer is no. If the module is wired correctly and working correctly the data should just show up in WX memory.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

plcnut

  • Hero Member
  • *****
  • Posts: 814
    • premiersi.com
Re: Do More thermocouple
« Reply #5 on: April 23, 2013, 09:45:40 AM »
Double check the wiring, and make sure the PLC is in Run mode. (I don't want to admit how many times I've had problems, and it was because I was in program mode  :o )
Also Is the PLC seeing the module in the configuration menu?
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
http://premiersi.com

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 261
    • Host Engineering, Inc.
Re: Do More thermocouple
« Reply #6 on: April 23, 2013, 03:13:34 PM »
that module also requires an external 24V connection, make sure it's securely attached, and that the polarity is correct.
Good design costs a lot. Bad design costs even more.

Rastus81

  • Jr. Member
  • **
  • Posts: 15
Re: Do More thermocouple
« Reply #7 on: April 23, 2013, 08:30:45 PM »
Thankyou for your replies.

I tried a new thermocouple and the WX register produced a reading.

Although the original thermocouple worked ok in my meter. Maybe i didn't have it secured well enough under the terminal screw.

I wonder if there is an input for open circuit detection?

Thanks again.
Rastus

plcnut

  • Hero Member
  • *****
  • Posts: 814
    • premiersi.com
Re: Do More thermocouple
« Reply #8 on: April 23, 2013, 09:11:44 PM »
It will be Xn. See page 6-27 of the manual.
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
http://premiersi.com