They only to stop is to leave a nop rung.
And you have to be careful with this one. Technically, NOP means NUL-OPERATION or NO-OPERATION, hence
STR X0
OUT Y0
NOP
OUT Y1
when drawn, it looks like this:
.X0 Y0
-] [-----( OUT )
---------( NOP )
Y1
---------( OUT )
Y1's state is NOT "ALWAYS ON" (even though it's tied to the power rail), but on the STATE of X0!!!
Do-more WARNS you with our Program Check utility:
W101 Rung mmm#rrr is missing input logic, powerflow state will be based on previous rung's power flow state.
see attached screen shot of Program Check output