Topic: DMD0022 FREQCNT - Frequency Counter |
|
|
|
|
|
The Frequency Counter (FREQCNT) instruction is used to convert the rate of a series of pulses to engineering units by sampling the counts for a period of time, normalizing that value to the desired time base, then scaling that value to the desired engineering units. This type of scaling is typically done for speed, flow rate, velocity, etc..
This instruction operates in a similar manner to the Rate Scaling and Position Scaling operations in the CTRIO modules.
The Frequency Counter is always enabled, meaning that the output value is constantly being generated based on the frequency of the input pulses. This means the output value is constantly being updated. |
|
Parameters:Note: Use the F9 key (Element Browser) or Down-Arrow key (Auto-Complete) at any time to see a complete list of the locations that are valid in the current field of the instruction.
Counter Struct - designates a unique Counter structure that this instruction will use. This can be any of the system defined Counters (CT Data Block), or any user defined Counter.
Sample Time
- specifies the amount of time to sample the incoming pulse rate. The Sample
Time is specified using the Time format (HH : MM : SS : mmm). The maximum
Sample Time value in this form is 569 hours, 31 minutes, 23 seconds, and
647 milliseconds. If needed, the value entered for the Sample Time will
be normalized to its standard value. For example, if you entered a value
of 97 Seconds, that value will be converted and displayed as 1 Minute
and 37 Seconds.
Frequency Units - specifies
the output scaling factor
Filter - enables a filtering
algorithm that is applied during the calculation that defines how much
'weight' the current-value is given versus the latest-calculated-value.
Filtering acts as a data smoothing function, balancing stability versus
the responsiveness of the calculated value as it responds to changes in
the input pulse rate. A large filter value gives more weight to the latest-calculated-value
(and hence less weight to the current-value), producing a more stable
value that responds more slowly to changes in the input pulse rate. A
small filter value gives less weight to the latest-calculated-value (and
hence more weight to the current-value), producing a less stable value
but it responds more quickly to changes in the input pulse rate.
Scale Factor - optionally applies an additional scaling factor to the calculated value, for example, to convert counts per second to engineering units like gallons per seconds.
Output - designates a location to store the output value. This can be any writable REAL location.
|
|
|
|
|
Status Display:The yellow triangle in the upper left corner indicates this is a Multi-Scan instruction.
The first input leg is the Count Input. The gray triangle at the right
end of an input leg indicates the input is edge
triggered
The second input leg is the Count Reset (RST). When this input logic is ON, the Frequency Counter's output value will be set to 0.0.
|
|
|
|
|
See Also:
|
|
|
|
|
Rung Example:
|
|
|
|
|