Topic: DMD0002

ALHILO - High/Low Alarm


The High/Low Alarm instruction (ALHILO) monitors the Input and sets the appropriate alarms based on the alarm limit values.

 

When entering the alarm limit values, ensure that the High-High Limit value is greater than the High Limit value, which must be greater than the Low Limit value, which must be greater than the Low-Low Limit value.

 

When designating the alarm bits, ensure that all of the alarm bit references are unique.

 

The alarm states are inclusive. Both the High-High Limit and High Limit alarms will be ON when the input value is greater than or equal to the High-High Limit. Both the Low Limit and the Low-Low Limit alarms will be ON if the input value is less than or equal to the Low-Low Limit.

 

Parameters:

Note: Use the F9 key (Element Browser) or Down-Arrow key (Auto-Complete) at any time to see a complete list of the memory locations that are valid in the current field of the instruction.

 

Input  - identifies the memory location to monitor. This can be any readable numeric location.

 

HH Limit, H Limit, L Limit and LL Limit - identify the alarm limit values. These values can be any constant value or any readable numeric location.

 

HH Alarm, H Alarm, L Alarm and LL Alarm - identify the alarm bits. These values can be any writable bit locations.

 

Note: Each Alarm/Limit pair is optional. Leave both fields empty to indicate that Limit is not being used, otherwise enter values for both fields to indicate that Limit is used.

 


Status Display:

When the ladder status is ON, in addition to the standard status values being displayed, the High/Low Alarm instruction also displays two "mini-trends" that show the instruction's values graphically.

The top graph shows the input value and the four Alarm limits.

The bottom graph shows the four Alarm output BITs

 

The mini-trend display can be disabled in the View-> Options menu, select the Ladder tab, then uncheck the Show Trend Status selection.


See Also:

 


Related Topics:

 


Rung Example: