Thanks, Bernie and BobO.
I see Bernie caught the 0 or 100 hang before I got back from testing these in the sim. Rather than the clamp, I put an OFFDTMR around the MATH with a falling edge timer contact around the rising edge TIMEPROP output. Then if it goes too long or on first run, it "watchdogs" the input update. Except for that, Bernie's example works fine (the ST4 seems OK regardless of contact type) and I am truly puzzled because I thought I had already tried this suggestion.
BobO's will hang for the same conditions. I see this one running without the extra transitions also, but I'm pretty sure I don't understand why the second branch doesn't cause an issue.
Regardless, if I can keep the TIMEPROP I'll be happier, I didn't mention some of the zones are heat AND cool, and the fans are on contactors. Plus they need to come on, and stay on longer, the more the PID output is below 50%. I was looking at LERP to solve some of that scaling, but the TIMEPROP is cleaner.
Thank you Bob! I would really appreciate this. A minor glitch on run transition is not a big deal.