Author Topic: HELP !!!!! H2-CTRIO I/O Map word output range not matching  (Read 5651 times)

eric14779

  • Full Member
  • ***
  • Posts: 30
I am working on set up of my H2-CTRIO in a DL205 PLC with a DL250-1 CPU slot #1 I am using the post that Greg the moderator wrote on October 31, 2008, at 04:48:10 pm ยป ( How do you program a Stepper with encoder for feedback. )

and I am not getting the same range for the Word OUTPUT range   Start is at V2030   My range is V2030-V2053 ??

not the V2030-V2061  as described in this post as well as the manual...

What is going on ??

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: HELP !!!!! H2-CTRIO I/O Map word output range not matching
« Reply #1 on: May 09, 2012, 03:28:08 PM »
Check that you have the latest version of CTRIO Workbench. The latest one allocated more input and oputput space.
An output is a PLC's way of getting its inputs to change.

eric14779

  • Full Member
  • ***
  • Posts: 30
Re: HELP !!!!! H2-CTRIO I/O Map word output range not matching
« Reply #2 on: May 10, 2012, 07:27:53 AM »
b_carlton

Yep as always you are Correct !!!

updated and now I get the proper range on the outputs

Thank You...