Topic: Use of LVDT for closed loop feedback versus rotary Encoder (Read 1004 times)
opburg89
Newbie
Posts: 2
Use of LVDT for closed loop feedback versus rotary Encoder
«
on:
July 23, 2026, 08:29:15 PM »
Good afternoon,
Is there any information for using an LVDT transducer with a 4-20mA analog output signal instead of a standard rotary style encoder for the closed-loop feedback
for a single Axis setup configured within Do-more? It appears if I'm reading correctly that you need to use a standard pulsed rotary encoder for the position/velocity feedback input?
The application we are using it on has a Hydraulic cylinder with an integrated 4-20mA LVDT transducer analog feedback and the cylinder is being controlled by a +/-10vdc
hydraulic proportional valve. Thanks in advance!
Logged
MikeS
Host Moderator
Hero Member
Posts: 270
Re: Use of LVDT for closed loop feedback versus rotary Encoder
«
Reply #1 on:
July 28, 2026, 08:35:49 AM »
You're correct that our Axis implementation is directed toward motor control, so pulse inputs and pulse outputs are the expected I/O.
Your inputs and outputs are 4-20mA and +/-10VDC, which is more attuned to standard PID loop control.
Logged