Kristjan

  • Sr. Member
  • ****
  • Posts: 88
    • Idnadartaekni ehf
BRX36 / Burnt components
« on: May 24, 2023, 12:05:27 PM »
We have lately had two BX-DM1E-36ER3-D literally going up in smoke. Two different sites.

See attached picture of the two PCBs. What are the burnt components? What can cause this?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX36 / Burnt components
« Reply #1 on: May 24, 2023, 12:38:51 PM »
We have lately had two BX-DM1E-36ER3-D literally going up in smoke. Two different sites.

See attached picture of the two PCBs. What are the burnt components? What can cause this?

Yuk. Looks like power supply parts. I'll get more info from engineering.

Please send them to us. We'll turn them around ASAP. PM me and we can exchange relevant info.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Kristjan

  • Sr. Member
  • ****
  • Posts: 88
    • Idnadartaekni ehf
Re: BRX36 / Burnt components
« Reply #2 on: May 24, 2023, 12:49:36 PM »
Thanks!

I am very interested in what engineering thinks because we have replaced both with new BRXs and everything looks good so far. But I would be very embarrassed if they were to burn a second time.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX36 / Burnt components
« Reply #3 on: May 24, 2023, 12:50:21 PM »
Thanks!

I am very interested in what engineering thinks because we have replaced both with new BRXs and everything looks good so far. But I would be very embarrassed if they were to burn a second time.

You and me both.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX36 / Burnt components
« Reply #4 on: May 24, 2023, 01:05:33 PM »
Thanks!

I am very interested in what engineering thinks because we have replaced both with new BRXs and everything looks good so far. But I would be very embarrassed if they were to burn a second time.

Engineering says "Not sure. Would like to get them back to do failure analysis."

So yeah, if possible we'd like to get them back to analyze and repair.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Kristjan

  • Sr. Member
  • ****
  • Posts: 88
    • Idnadartaekni ehf
Re: BRX36 / Burnt components
« Reply #5 on: March 15, 2024, 07:57:06 AM »
Opening up this issue again, since I am experiencing the same on another location.

A BRX36 has been in operation for 2+ years with no problems. It suddenly stopped working and by inspecting the insides, we see the same power component burnt. Was there any conclusion from your research on the two units that we returned?

The weirdest thing is that we installed a new PLC and a new power supply and the new PLC immediately overloads the power supply (high frequency noise from PS and DC OK light off). We only connected the new PLC to power for a short period and there is nothing burnt inside.

New PLC:
HW re 8A 5A 7A
Date code 0224
Serial # 02248A5A7A30A146

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX36 / Burnt components
« Reply #6 on: March 15, 2024, 10:13:13 AM »
Opening up this issue again, since I am experiencing the same on another location.

A BRX36 has been in operation for 2+ years with no problems. It suddenly stopped working and by inspecting the insides, we see the same power component burnt. Was there any conclusion from your research on the two units that we returned?

The weirdest thing is that we installed a new PLC and a new power supply and the new PLC immediately overloads the power supply (high frequency noise from PS and DC OK light off). We only connected the new PLC to power for a short period and there is nothing burnt inside.

New PLC:
HW re 8A 5A 7A
Date code 0224
Serial # 02248A5A7A30A146

I believe in the older unit we determined that there was a part that had wandered a bit and caused two things to turn on at the same time that shouldn't do so. We made a design change to eliminate the issue.

No clue on the new unit, but we would love to get it back to fix it and do a failure analysis.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: BRX36 / Burnt components
« Reply #7 on: March 15, 2024, 03:10:13 PM »
Does the issue only apply to 36s?
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX36 / Burnt components
« Reply #8 on: March 15, 2024, 03:39:49 PM »
Does the issue only apply to 36s?

No, pretty much everything except the modulars. It isn't a new thing and I don't think the failure rate has been excessively high, but they do cluster for some odd reason. Makes me wonder if there is something environmental that tends to expose it. I don't remember the exact details, but I think it is a couple of components in the same package that are supposed to be matched and occasionally drift. Power supply design is mostly science, but there is definitely some finicky art to it.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO