EDIT: Added to wrong thread, but still relevant...
https://forum.hosteng.com/index.php?topic=3425.0The timing of this is odd, as the last time we visited a similar issue was near same time just a few months back!
This morning (2AM PST...) client lost comms with only one site, called Moonbeam. All status indicators (Success, Failure) on MRX/MWX remained off.
Set for 30 & 60 second intervals on the instructions.
All other sites worked without issue (BRX is Master to 5 DL-06 PLCs, SCADA requests all data from BRX through a single connection).
Direct from SCADA to Moonbeam worked without issue; VPN to Moonbeam via DirectSOFT worked fine.
The connection count wasnt the first thought, but noticed the Idle Time on the device was constantly at 46 and Open, while all the other devices would quickly cycle Open to Closed.
Tried Reinitialize IO, Program/Run transitions, changing IP address of the instruction (it was early, seemed like something to try).
Only solution was a power-cycle of the BRX, comms returned immediately.
Did the suggestions in this thread (16 concurrent connections and low timeout for connections) as a possible mitigation effort.
We have other units with similar code base, but those use the Serial devices (Internal or POM) and have not had this issue at all. Definitely something with Ethernet.