DL06/260 MRX command
« on: August 12, 2014, 01:20:31 PM »
How do you know if the MRX command was successful, the box command doesn't have a success bit?

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: DL06/260 MRX command
« Reply #1 on: August 12, 2014, 01:29:13 PM »
Refer to the 'Busy' and 'Error' bits for the port you are using.

I place MRX/MWX commands in a stage and, upon triggering, JMP to a following stage where the 'Busy' and 'Error' bits determine the next action.