Author Topic: Do-More PLC not Updating VFD speed  (Read 12036 times)

Saturn_Europa1

  • Jr. Member
  • **
  • Posts: 19
Do-More PLC not Updating VFD speed
« on: February 13, 2024, 05:04:41 AM »
I have a Do-More PLC controlling 6 GS-2 drives through GS-EDRV100s.  The PLC has a H2-ECOM100 ethernet module and the CPU is a H2-DM1E. 
 
The Do-More software is v2.4. I am not sure of the exact firmware in the PLC.

The PLC controls the speed on the drives through the GS-EDRV100s.  The speed inputs to the PLC is done through a C-More EA9 8" touch screen.  Once in a while the speed on the drives will not update.  I will enter the desired speed, the set point on the C-More will change but the drives will not respond to the new speed set point.

Any idea of what could be causing this?   

 




Saturn_Europa1

  • Jr. Member
  • **
  • Posts: 19
Re: Do-More PLC not Updating VFD speed
« Reply #1 on: February 13, 2024, 05:18:29 AM »
I forgot to add that the only solution I have found is cycling power to the PLC.  When you cycle power to the PLC it also cycles power to the C-mores and the GS-EDVR100s. 

I tried cycling power to the the GS-EDVR100s alone but this did not fix the problem. 

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Do-More PLC not Updating VFD speed
« Reply #2 on: February 13, 2024, 10:01:27 AM »
At the very least I'd get the PLC to the latest firmware. Current is 2.9.8 and we are releasing 2.9.9 shortly.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Saturn_Europa1

  • Jr. Member
  • **
  • Posts: 19
Re: Do-More PLC not Updating VFD speed
« Reply #3 on: February 13, 2024, 10:33:03 PM »
Someone told me not to do an update because we would lose communication with the C-Mores and the ethernet network.  This doesnt make sense to me.  Have you heard of anything like this? 

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Do-More PLC not Updating VFD speed
« Reply #4 on: February 13, 2024, 10:37:37 PM »
Someone told me not to do an update because we would lose communication with the C-Mores and the ethernet network.  This doesnt make sense to me.  Have you heard of anything like this?

No clue why that would be.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

rlp122

  • Sr. Member
  • ****
  • Posts: 92
Re: Do-More PLC not Updating VFD speed
« Reply #5 on: February 13, 2024, 10:54:49 PM »
Someone told me not to do an update because we would lose communication with the C-Mores and the ethernet network.  This doesnt make sense to me.  Have you heard of anything like this?

You are going to get a pause while the controller is updating, but that is all.  I suppose if you are using the GS-EDRV100's as remote control you might get a reset depending on your settings, but it will pick back up.  I wouldn't do it while you are running anything major, but that's just me.