Author Topic: Do-More BRX Ethernet IP EDS File from RFID Tracking Hardware  (Read 6323 times)

PLC4SKI

  • Newbie
  • *
  • Posts: 1
Do-More BRX Ethernet IP EDS File from RFID Tracking Hardware
« on: November 18, 2021, 07:44:04 PM »
Hello,

Working on a neat application to setup the BRX to communicate over Ethernet IP to a ifm DTE102 
RFID Reader over Ethernet IP in order to read the UID of tags passing by on a conveyor.

Having issue with decoding the EDS file from the Manufacturer of the ifm DTE102 and not clear from their documentation on the CIP structure for reading the UID of the tags.

I was able to setup the BRX Ethernet IP Communications to get the MAC address of the ifm DTE102 following the example on page
28 of the manual https://www.ifm.com/mounting/706357uk.pdf using the EIPMSG Instruction Class:0xF6  Instance:0x1  Attribute:3

( From Page 28 of Manual )
4. Reading the MAC address via the EtherNet/IP Ethernet link object
The Ethernet link object, 0xF6, instance 2, attribute 3 returns the MAC address of the device with a length
of 6 Bytes.
Example: 00 02 01 40 02 5E

Attached is the EDS file from the manufacturer ( had to change the extension to .txt for posting on the forum )

Any guidance greatly appreciated,

God Bless !









MAEdwards

  • Sr. Member
  • ****
  • Posts: 59
Re: Do-More BRX Ethernet IP EDS File from RFID Tracking Hardware
« Reply #1 on: November 22, 2021, 11:23:45 AM »
Based on the EDS and Manual...

Use the following information to WRITE Data to the DTE102:
  • Class: 0x04
  • Instance: 0x64
  • Attribute: 0x03
  • Service: Set_Attribute_Single 0x10

Use the following information to READ Data from the DTE102:
  • Class: 0x04
  • Instance: 0x65
  • Attribute: 0x03
  • Service: Get_Attribute_Single 0x0E

The EDS file indicates that both Assemblies Instances 100 (0x64) and 101 (0x65) are 80 bytes in size.  This can be confirmed by executing a Get_Attribute_Single service to Attribute 4 of both Assembly 100 and 101.  The manual appears to confirm this.

Mapping appears to be the following:

Assembly Instance 100 (0x64)
  • Bytes 00-19: IO 1 Data Request
  • Bytes 20-39: IO 2 Data Request
  • Bytes 40-59: IO 3 Data Request
  • Bytes 60-79: IO 4 Data Request

Assembly Instance 101 (0x65)
  • Bytes 00-19: IO 1 Data Response
  • Bytes 20-39: IO 2 Data Response
  • Bytes 40-59: IO 3 Data Response
  • Bytes 60-79: IO 4 Data Response

To get the UID, I believe you need the following:
  • Mode: RWH_RW
  • Request: Transition Byte 0 Bit 3 from 0 to 1.  The rising edge should trigger the RD request.
  • Response: The UID length will reside in Byte 2.  The actual UID will reside in Bytes 3 through 17.
This is based on IO 1 Data.  Byt offsets should be adjusted for IO 2, 3, and 4.

Please keep in mind, I do not have this IFM device, nor have I ever used it.  Therefore, all suggestions are based on vendor documentation.  I am unable to confirm the validity of any of this.  I hope this points you in the right direction.