programming through port 2
« on: August 26, 2008, 05:55:52 PM »
Can you program plc dl06 through port 2? I am doing this  to determine the status of port 2

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3601
  • Darth Ladder
Re: programming through port 2
« Reply #1 on: August 26, 2008, 06:38:14 PM »
Yes you can program through port 2 (if it's set to one of the protocols DirectSOFT can work with).  I have had a problem with poor performance programming through port 2 if an MMI is connected to port 1 at the same time, but never the other way around.

You say you want to determine the status of port 2.  You don't have to connect to port 2 to see its configuration if that's what you mean.  While connected to port 1, select PLC --> Setup --> Setup Sec. Comm Port...   and you can inspect and edit the configuration as far as protocols supported, baud rate, parity, turnaround delay, and so on.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

mo2004

  • Jr. Member
  • **
  • Posts: 14
Re: programming through port 2
« Reply #2 on: August 27, 2008, 11:21:09 AM »
 Can I use the link wizard to establish programming through port 2?


The issue is i am trying to test ASCII strings with Microsoft HyperTerminal.
Automation direct document AN-MISC-020. I did not have any luck.

The setup is exact from my end. Cable used is D2-DSCBL-1

so to eliminate problems I am trying to program through port 2 using the same cable. This will tell me if the port2 have any problem. The cable is brand new.

thank you for all your help ???

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3761
    • Host Engineering
Re: programming through port 2
« Reply #3 on: August 27, 2008, 11:35:17 AM »
Port 2 cannot be used as an ASCII (aka Non-Sequence) protocol and a programming port at the same time.  Are you trying to test ASCII strings through Port 2 AND use DirectSOFT through Port 2?

mo2004

  • Jr. Member
  • **
  • Posts: 14
Re: programming through port 2
« Reply #4 on: August 27, 2008, 12:26:32 PM »
I apologize for not making my self clear.
They are not done at the same time.
Typically I will try sending ASCII off port 2, and program the PLC  through port 1
This is a temporary set up to test connectivity of port 2.

mo2004

  • Jr. Member
  • **
  • Posts: 14
Re: programming through port 2
« Reply #5 on: September 04, 2008, 05:02:21 PM »
Port 2 of the PLC was bad I changed the PLC and every thing worked fine. :)