Hello,
I have read in some of the posts that the BX-P-ECOMLT has certain limitations. I am trying to use it as a Modbus TCP server, but I cannot get it to work. The main Ethernet port works just fine but not the ECOMLT port. According to the BRX manual, it says it supports Modbus TCP server, but I did not find an option to enable the Modbus TCP server for the ECOMLT anywhere, just an option to enable it in the main port.
Any thoughts?
Thanks,
Miguel
-
The initial firmware release didn't support it, it was added after launch, so make sure you're up to date. No configuration is required in DmD, it just works.
-
Thanks for the prompt reply. I was not aware that the firmware in BX-P-ECOMLT is upgradeable with NetEdit. I will give this a shot.
Regards,
Miguel
-
Thanks for the prompt reply. I was not aware that the firmware in BX-P-ECOMLT is upgradeable with NetEdit. I will give this a shot.
Regards,
Miguel
Yes, it is. Let us know if that fixes it for you.