News:

  • June 12, 2026, 09:32:19 PM

Login with username, password and session length

Author Topic: D0-06 Controling Timer Value through I/O  (Read 11593 times)

Jersey Red

  • Newbie
  • *
  • Posts: 1
D0-06 Controling Timer Value through I/O
« on: January 11, 2012, 07:30:05 AM »
I am using 2 BCD Thumb switches ( address x100 - x107 ) to control a on delay timer value. I need a basic flow of moving and converting the data for the timer.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: D0-06 Controling Timer Value through I/O
« Reply #1 on: January 11, 2012, 09:02:21 AM »
Let's assume that a timer has been set up with its preset in V2000.

The rung to move the value from the thumbwheel switches to the preset would be

LDF X100 K8
OUT V2000
An output is a PLC's way of getting its inputs to change.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3607
  • Darth Ladder
Re: D0-06 Controling Timer Value through I/O
« Reply #2 on: January 11, 2012, 04:26:07 PM »
If you can dedicate the entire word to the thumbwheels, you can just refer to VX100.  I got to do that ONE time.  Serendipitous!
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

ATU

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 2126
  • YKPAIHA
    • ATU, Inc.
Re: D0-06 Controling Timer Value through I/O
« Reply #3 on: January 11, 2012, 07:09:24 PM »
Sounds like a homework problem to me.