News:

  • June 11, 2026, 06:11:08 AM

Login with username, password and session length

Author Topic: Upload program from PLC witout a copy on the PC  (Read 8935 times)

upstream

  • Newbie
  • *
  • Posts: 1
Upload program from PLC witout a copy on the PC
« on: September 10, 2009, 01:35:05 PM »
Hi all,

How can I upload a program from a Directlogic 405 PLC (D4-450 CPU) without having a copy of the program on my PC?

thanks in advance...

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: Upload program from PLC witout a copy on the PC
« Reply #1 on: September 10, 2009, 02:12:43 PM »
Yes, assuming it's not password protected. Of course you wont have any nicknames or comments.
An output is a PLC's way of getting its inputs to change.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3607
  • Darth Ladder
Re: Upload program from PLC witout a copy on the PC
« Reply #2 on: September 10, 2009, 02:14:11 PM »
Method 1:  Get a comm link configured and talking to the PLC, (using "Auto" makes this easier when applicable).  Then double click on the link, which should have a green icon.  Directsoft (programming app) will open with the uploaded program in the ladder window.

Method 2:  Get the comm link configured and working.  Open a Directsoft window and create a new application for the model PLC you're connected to.  Go online with the PLC.  Since the Directsoft app contents and the PLC are not equal, you'll get a dialog asking which program to use.  Click "Use PLC", and the code will be displayed in the ladder window.

After using either method, select File -> Save Project As, and save to disk on your programming terminal.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.