Topic: DMD0550
CTRIO Module Configuration - Configure IO |
|
Configure IO Overview:
To get to the CTRIO Module Configuration - Configure IO dialog:
Follow this menu path: PLC
--> System Configuration --> Module Configuration(s).
This pulls up the System Configuration dialog.
Double-click on the CTRIO to configure. This pulls up
the Edit CTRIO/CTRIO2 Configuration dialog.
Press the <Configure
I/O> button.
Here is where the input and output functions of the
CTRIO are defined.
Channel 1 / Channel
2 - These tabs allow the
configuration of all 4 of each Channel's inputs (A, B, C, D) and correspond
directly with the CTRIO's input terminals (1A-1D & 2A-2D). The current
options for a given input are displayed in the window, however, these
options change dynamically as different options are chosen.
Function 1 / Function
2 - These boxes change showing further options for the input functions
chosen.
Outputs
- This allows the configuration of all 4 of the outputs (0, 1, 2, 3) and
correspond directly with the CTRIO's output terminals (Y0-Y3). The current
options for a given output are displayed in the window, however, these
options change dynamically as different options are chosen.
Configuring CTRIO Inputs
There are basically 10 input settings but they
are not supported on all inputs and some are mutually exclusive of others.
However the configuration dialog will change dynamically to show which
ones are available:
Configuring CTRIO Outputs
There are basically 5 output settings but they
are not supported on all outputs and some are mutually exclusive of others.
However the configuration dialog will change dynamically to show which
ones are available:
Unassigned - The output has no function.
Raw - Allows the Do-more
controller to directly turn this output ON/OFF. Click
here for details.
Discrete on Ch1/Fn1 / Discrete on Ch1/Fn2
/ Discrete on Ch2/Fn1 / Discrete on Ch2/Fn2 - Allows the output
to be used in conjunction with a CTRIO input function. Click
here for details.
Discrete on Pulse Out 0/1 / Discrete on Pulse
Out 2/3 - Allows the output to be used in conjunction with a CTRIO
pulse output function. Click
here for details.
Pulse (Step/Dir) / Pulse (CW/CCW) -
Uses two outputs (0 & 1 or 2 & 3) where the first one is a pulse
output and the second one is a direction output bit (step/dir) or where
the first one generates pulses for clockwise motion and the second one
generates pulses for counter-clockwise motion (cw/ccw). Click
here for details.
|
|
CTRIO Input Functions:
Counter Function
This function is available for Ch1A, Ch1B, Ch2A &
Ch2B inputs. It counts single-ended pulses. By default there are 4 basic
options available:
(1) Up / Down (button) - Pressing this
button changes whether the counter counts up or down.
(2) Edge (button) - Pressing this button
changes whether the rising edge or falling edge is counted.
(3) Scaling (button) - Pressing this button
allows the count value to be scaled and calls up the Scaling Wizard. Click
here for help with scaling.
(4) Reset Value - Clicking in the data
input field allows a count reset value to be entered. This is the value
that will be loaded into the counter when a reset (hardware or software)
occurs. It must be a value between -2,147,483,648 and +2,147,483,647.
The raw count value (if there is no scaling) is reported in the CTRIO structure. For example:
Other interfaces to the count function in the CTRIO structure are, for
example:
Also a software reset bit can be set to reset the count to the reset
value, for example:
The counter function can be further modified by the C & D inputs
and will be covered in detail below. These are the already-mentioned Reset Fn1 / Reset Fn2, Capture Fn1
and Inhibit Fn1
input functions.
|
|
Quad Counter
This function is available for Ch1A/Ch1B & Ch2A/Ch2B
input pairs. It counts quadrature encoder pulses. By default there are
3 basic options available:
(1) Multiplier (button) - Pressing this
button cycles through 1X, 2X or 4X choices.
1X - counts
leading edge of pulse on input A.
2X - counts
leading and falling edges of pulse on input A.
4X - counts
leading and falling edges of pulses on both input A & input B.
(2) Scaling (button) - Pressing this button
allows the count value to be scaled and calls up the Scaling Wizard. Click
here for help with scaling.
(3)
Reset Value - Clicking in the
data input field allows a count reset value to be entered. This is the
value that will be loaded into the counter when a reset (hardware or software)
occurs. It must be a value between -2,147,483,648 and +2,147,483,647.
The raw count value (if there is no scaling) is reported in the CTRIO
structure. For example:
Other interfaces to the count function in the CTRIO structure are, for
example:
Also a software reset bit can be set to reset the count to the reset
value, for example:
The quad counter function can further be modified by the C & D inputs
which will be covered in detail below. These are the already-mentioned
Reset Fn1, Capture Fn1 and Inhibit Fn1 input functions.
|
|
Pulse Catch
This function is available for Ch1C, Ch1D, Ch2C &
Ch2D inputs. This function qualifies a short-duration pulse by a minimum
width in microseconds and outputs a software bit of millisecond length.
This allows the Do-more controller
to catch unusually quick pulses that normal input modules would miss.
By default there are 3 basic options available:
(1) Pulse Edge (button) - Pressing this
button changes whether the input looks for a rising or falling edge pulse.
(2) Minimum Width In - This is the minimum
pulse width in microseconds you want to capture. Transients shorter than
this duration will be ignored. This value must be between 1 and 2,147,483,647
microseconds.
(3) Pulse Out Width - This is the duration
in milliseconds you want the CTRIO to send in response to the input pulse.
This value must be between 1 and 2,147,483,647 milliseconds.
To enable the function once it is configured, a bit in the CTRIO structure
must manually be set ON. For example:
Once the function is enabled, then when a pulse has been detected, this
is reported in the CTRIO structure. For example:
When the pulse is qualified then a bit in the CTRIO structure is set
for the Pulse Out Width duration.
For example:
|
|
Edge Timer
This function is available for Ch1C, Ch1D, Ch2C &
Ch2D inputs. This function measures the time from edge to edge of a pulse.
By default there are 4 basic options available:
(1) Edges Definition (button) - Pressing
this button cycles through 4 choices of how the time will be measured:
Rising edge to rising
edge
Rising edge to falling
edge
Falling edge to rising
edge
Falling edge to falling
edge
(2) Scaling (button) - Pressing this button
allows the count value to be scaled and calls up the Scaling Wizard. Click
here for help with scaling.
(3) Free Run - Checking this box causes
the edge timer to continuously arm itself after each measurement resulting
in a continuous (moving average) measurement. If unchecked, the edge timer
must be manually armed for each measurement.
(4) Timeout - Checking this box allows
a value to be entered in the Timeout data field. The purpose of this option
is when the first edge is detected, if it takes too long (the Timeout
value) for the second edge to occur, then a timeout bit is set. This keeps
the edge timer from getting "stuck" just waiting for that second
edge. The Timeout value must be between 1 and 2,147,483,647 microseconds.
To enable the function once it is configured,
a bit in the CTRIO structure must manually be set ON. For example:
Once the function is enabled, then when
a pulse has been detected, this is reported in the CTRIO structure. For
example:
When the first edge is detected the timer
starts running and is reported in the CTRIO structure. For example:
If the second edge is detected a successful
measurement and its value are reported in the CTRIO structure. For example:
$CTRIO_000_C1F1.CaptureComplete
- Channel 1 function 1, second edge detected and measured bit
$CTRIO_000_C1F1.iReg2
- Channel 1 function 1, signed integer captured time value in microseconds
If Timeout is enabled and the second edge
is not detected before the Timeout value is reached, this is reported
in the CTRIO structure. For example:
If free run is not enabled, then the edge
timer must be re-enabled to measure another edge time. If free run is
enabled the edge timer re-enables itself.
|
|
Dual Edge Timer
This function is available for Ch1C/Ch1D, Ch1D/Ch1C,
Ch2C/Ch2D & Ch2D/Ch2C input pairs. This function measures the time
from the edge of a pulse on one input to the edge of a pulse on a second
input. By default there are 4 basic options available:
(1) Edges Definition (button) - Pressing
this button cycles through 4 choices of how the time will be measured:
Rising edge of one input
to rising edge on other input
Rising edge of one input
to falling edge on other input
Falling edge of one
input to rising edge on other input
Falling edge of one
input to falling edge on other input
(2) Scaling (button) - Pressing this button
allows the count value to be scaled and calls up the Scaling Wizard. Click
here for help with scaling.
(3) Free Run - Checking this box causes
the dual edge timer to continuously arm itself after each measurement
resulting in a continuous (moving average) measurement. If unchecked,
the dual edge timer must be manually armed after each measurement.
(4) Timeout - Checking this box allows
a value to be entered in the Timeout data field. The purpose of this option
is when the first edge is detected on the first input, if it takes too
long (the Timeout value) for the second edge to occur on the second input,
then a timeout bit is set. This keeps the dual edge timer from getting
"stuck" just waiting for that second edge. The Timeout value
must be between 1 and 2,147,483,647 microseconds.
To enable the function once it is configured, a bit in the CTRIO structure
must manually be set ON. For example:
Once the function is enabled, then when a pulse has been detected on
the first input, this is reported in the CTRIO structure. For example:
When the first edge is detected the timer starts running and is reported
in the CTRIO structure. For example:
If the second edge is detected a successful measurement and its value
are reported in the CTRIO structure. For example:
$CTRIO_000_C1F1.CaptureComplete
- Channel 1 function 1, second edge detected and measured bit
$CTRIO_000_C1F1.iReg2
- Channel 1 function 1, signed integer captured time value in microseconds
If Timeout is enabled and the second edge is not detected before the
Timeout value is reached, this is reported in the CTRIO structure. For
example:
If free run is not enabled, then the dual edge timer must be re-enabled
to measure another dual edge time. If free run is enabled the dual edge
timer re-enables itself. |
|
Reset Count
Reset Fn1 is available
on Ch1C or Ch2C only if a counter or quad counter has been configured
for function 1. In other words, only if Ch1A or Ch2A are configured as
a counter, or Ch1A/Ch1B or Ch2A/Ch2B are configured as a quad counter.
This function modifies the counter/quad counter function box by adding
a button. It allows the C input to reset the count value to the reset
value. By default there is one option:
Reset Edge (button)
- Pressing this button configures the reset to execute either on the rising
edge, falling edge, high level or low level of input C. The edge reset
sets the current count to zero on the specified edge (rising or falling)
of the reset pulse. The level reset resets the count to zero (as long
as the reset pulse is held high (or low depending on configuration)).
When the reset pulse is not at level anymore, the count resumes.
Reset Fn2 is available on Ch1D
or Ch2D only if a counter has been configured for Ch1B or Ch2B respectively.
It is functionally equivalent to Reset
Fn1.
Note:
It is also possible to reset the count using the CTRIO's own channel/function
structure member bit (.Reset). When this bit is ON, the count is reset; when
this bit is OFF, the counter function is free to count.
|
|
Capture Count
Capture Fn1 is available
on Ch1D or Ch2D only if a counter or quad counter has been configured
for function 1. In other words, only if Ch1A or Ch2A are configured as
a counter, or Ch1A/Ch1B or Ch2A/Ch2B pairs are configured as a quad counter
will the capture function be available. This function modifies the counter/quad
counter function box by adding a button. It allows input D to snapshot
the count on function 1 and store it into a CTRIO structure register.
By default there is one option:
This function works in the following manner:
The capture function must be enabled by turning ON the
channel/function capture enable structure member (e.g. $CTRIO_000_C1F1.EnableCapture).
Once
the capture is enabled, the CTRIO monitors the Capture
Fn1 input.
When
the capture signal is seen on the input, the channel/function count capture
structure member is turned ON (e.g. $CTRIO_000_C1F1.CountCaptured)
Also,
when the capture signal is seen the CTRIO "snapshots" the current
count into the second CTRIO structure register (e.g. $CTRIO_000_C1F1.iReg2).
To
repeat a capture, the capture enable bit (e.g. $CTRIO_000_C1F1.EnableCapture)
must be turned OFF, then refer back to Step 1 above.
|
|
Inhibit Counting
Inhibit Fn1 is available
on Ch1D or Ch2D only if a counter or quad counter has been configured
for function 1. In other words, only if Ch1A or Ch2A are configured as
a counter, or Ch1A/Ch1B or Ch2A/Ch2B pairs are configured as a quad counter
will the inhibit function be available. This function modifies the counter/quad
counter function box by adding a button. It allows input D to inhibit
function 1 counter from counting pulses. By default there is one option:
When the inhibit signal is seen on input D, it causes the CTRIO function
1 counter to stop counting pulses. When the inhibit signal disappears,
counting will resume. |
|
Limit For Output
Limit Out 0 and Limit Out 2 are available on Ch1C, Ch1D,
Ch2C & Ch2D only if Output0/1 and Output2/3 are configured as either
pulse (step/direction) or pulse (cw/ccw). This function allows input C
and/or input D to be used in conjunction with a CTRIO pulse output instruction.
The CTRIO instructions that can utilize this feature are:
CTAXLIMT (CTRIO2
Axis Run Trapezoid w/Limits) - Because this instruction requires choosing
a limit.
CTRUNPOS (CTRIO
Run Position Mode) - If the profile being used in the instruction is:
CTRUNVEL
(CTRIO Run Velocity Mode) - If a limit is chosen in the instruction.
|
|
CTRIO Output Functions:
Raw Output
Raw is available on Out0,
Out1, Out2 & Out3. This function allows the Do-more
controller to directly turn this output ON or OFF via a CTRIO structure.
For example:
Setting ON or resetting this bit OFF directly causes the CTRIO output
to turn ON or go OFF. |
|
Discrete Output For
Input Function
Discrete on Chx/Fnx is
available on Out0, Out1, Out2 & Out3. This function allows the output
to be used in conjunction with a CTRIO input function and preset or to
be used by previously defined discrete output tables. This function modifies
the function box by adding a preset button. By default there can be 2
options (Preset mode and Level mode):
(1) Preset (button)
- If no default preset mode action is needed for this output, then there
is nothing else to do. If a default preset mode action is desired, then
pressing this button will pull up the Default Output Settings (Preset
Mode) dialog. By default this is set to None.
Any other setting on this dialog will be executed when the CTRIO is taken
from program to run mode, or powered up. Default preset mode actions are:
|
|
|
|

|
|
(2)
Level (button) - If a the Chx/Fnx
has been rate or interval scaled (note the ruler button now has arrows)
then it is possible to select a default behavior called level mode. This
mode would be commonly used to set an alarm for a rate or interval that
is too high or too low. Pressing the <Level> button will pull up
the Default Output Settings (Level Mode) dialog. By default this is set
to None. Any other setting on
this dialog will be executed when the CTRIO is taken from program to run
mode, or powered up. Default level mode actions are:
|
|

ON when value
is greater than level - the CTRIO output will come ON when the
rate- or interval-scaled count (or timer) value is greater than the Level
ON when value
is less than level - the CTRIO output will come ON when the rate-
or interval-scaled count (or timer) value is less than the Level
OFF when value
is greater than level - the CTRIO output will go OFF when the rate-
or interval-scaled count (or timer) value is greater than the Level
OFF when value
is less than level - the CTRIO output will go OFF when the rate-
or interval-scaled count (or timer) value is less than the Level
Level
- the rate- or interval-scaled count (or timer) value used for the action.
Notice also the 4-charater Engineering Units text field entered in the
rate or interval scaling wizard are shown to the right of the value.
Deadband - the percentage of the Level value in which there will be no CTRIO output
change. This is used to prevent CTRIO output chattering (rapidly toggling
OFF/ON) in case the rate- or interval-scaled count (or timer) value is
fluctuating too rapidly. Thus, for example, if the Default Level Command
was set to "ON when value is greater than level", the Level value is 500 and Deadband is set to 10.0% then when the scaled value
reaches 500, the output will come ON. But if at that point the scaled
value begins to go lower than 500, it will not turn back OFF until the
value reaches 450 (500 minus 10.0%).
|
|
Discrete Output
For Pulse Output Function
Discrete on Pulse Out x/x
is available on Out0, Out1, Out2 & Out3 but only if one output pair
(i.e. Out0/Out1 or Out2/Out3) is configured for Pulse Output. This function
allows the output to be used in conjunction with the other pulse output
pair and utilized by a previously defined discrete output table. This
works just like the Discrete Output For Input Function above with the
exception that the Preset or Level buttons are not supported.
|
|
Pulse Output
Pulse (Step/Dir) / Pulse (CW/CCW) is available on Out0/Out1 & Out2/Out3
pairs. This function allows two outputs to be used together where the
first one is a pulse output and the second one is a direction output bit
(step/dir) or where the first one generates pulses for clockwise motion
and the second one generates pulses for counter-clockwise motion (cw/ccw).
This function is used in conjunction with previously defined pulse profiles
and/or CTRIO Do-more instructions.
Previously defined pulse profiles and CTRIO Do-more
instructions that are used with pulse output:
CTAXCFG (CTRIO2 Axis
Configuration) - defines a pulse output behavior with the luxury
of not having to use a previously defined pulse profile.
CTAXDYNP (CTRIO2 Axis
Run Dynamic Position Mode) - uses a pulse output which was previously
defined by the CTAXCFG instruction
for asymmetrical linear trapezoidal movement where any number of
positions can be specified on-the-fly
CTAXDYNV (CTRIO2 Axis
Run Dynamic Velocity Mode) - uses a pulse output which was previously
defined by the CTAXCFG instruction
for asymmetrical linear trapezoidal movement where any number of velocities
can be specified on-the-fly
CTAXJOG (CTRIO2 Axis
Jog Mode) - uses a pulse output which was previously defined by
the CTAXCFG instruction for manual
asymmetrical linear trapezoidal movement forward or backward
CTAXLIMT (CTRIO2 Axis
Run Trapezoid w/Limits) - uses a pulse output which was previously
defined by the CTAXCFG instruction
for asymmetrical linear trapezoidal movement to specified physical limits
or positions
CTAXTRAP (CTRIO2 Axis
Run Trapezoid) - uses a pulse output which was previously defined
by the CTAXCFG instruction for
asymmetrical linear trapezoidal movement to specified target position
CTDYNPOS (CTRIO Run
Dynamic Position Mode) - uses a pulse output and one of the following
previously defined pulse profiles:
Dynamic Position
- symmetrical linear trapezoidal movement where any number of positions
can be specified on-the-fly
Dynamic Position
Plus - (CTRIO2 only) asymmetrical linear trapezoidal movement where
any number of positions can be specified on-the-fly with the additional
option of using a quadrature encoder attached to the CTRIO2 input channel
to provide the position
CTDYNVEL (CTRIO Run
Dynamic Velocity Mode) - uses a pulse output and the following
previously defined pulse profile:
CTRUNPOS (CTRIO Run
Position Mode) - uses a pulse output and one of the following
previously defined pulse profiles:
Trapezoid
- asymmetrical linear trapezoidal movement to a total number of pulses
S-Curve
- S-shaped movement to a total number of pulses
Symmetrical S-Curve
- symmetrical S-shaped movement to a total number of pulses
Home Search
- movement profile used to find a home position utilizing a CTRIO2 input
Free Form
- custom movement profile allowing any number of steps each having a number
of pulses to be output at a specified frequency
Trapezoid Plus
- (CTRIO2 only) asymmetrical linear trapezoidal movement to a run-time-provided
position with the additional option of using a quadrature encoder attached
to the CTRIO2 input channel to provide the position
Trapezoid w/Limits
- (CTRIO2 only) asymmetrical linear trapezoidal movement to a deceleration
trigger (a CTRIO2 input) and then to a stop trigger (a position or a CTRIO2
input) with the additional option of using a quadrature encoder attached
to the CTRIO2 input channel to provide the position.
CTRUNVEL (CTRIO Run
Velocity Mode) - uses a pulse output with the luxury of not
having to use a previously define pulse profile to specified physical
limits or positions
|
|