Topic: DMD0205 Arrays, Pointers, Tables and Indirect Addressing |
|
|
|
The most common form of addressing used in the Do-more controller is direct and symbolic. When a direct address is referenced by an instruction there is only one location in memory being targeted. The following are some examples of direct addressing: WX3 (analog input #3), WY26 (analog output #26), T17 (Timer #17), CT0 (Counter #0), D106 (signed DWord #106). Indirect Addressing:Indirect addressing allows the memory address used by an instruction to be varied so that it can point to more than one location at runtime. Used this way, one memory location stores a ”pointer” to another memory location. For example, if V17 has the value "37", then referencing D[V17] will return the value in the memory location D37. While this may initially increase the difficulty of troubleshooting, it has the advantage of greatly reducing the number of rungs and instructions needed to control a process.
The Do-more controller implements all of the built-in and user-created data blocks as arrays, so any of these data blocks can be indirectly addressed. And because all of the data blocks in the controller are limited to 65535 elements per block, the index value can only be in the range of 0 to 65535.
Only V memory locations can be used as indirect addresses.
The indirect address can optionally include an offset value. For example, if V17 has the value "37", then referencing D[V17 + 3] will return the value in the memory location D40. The Offset value is limited to a maximum of 63. Indirectly Addressing Bit LocationsAll of the bit-memory data blocks in the controller can be indirectly addresses. For example, if V17 has the value "37", then referencing C[V17] will return the value in bit location C37. Indirectly Addressing Numeric LocationsAll of the numeric data blocks in the controller can be indirectly addresses. For example, if V17 has the value "37", then referencing R[V17] will return the value in the memory location R37. Indirectly Addressing Structures and Structure FieldsStructures and individual structure fields can be indirectly addressed. For example, assume that V17 contains the value "37", then CT[V17] would be a valid reference to the structure used by Counter CT37, and CT[V17].Acc would be a valid reference to the Accumulator value of Counter CT37.
|
|
|
|
The Index Loop (FOR) instruction specifies that V17 will be used to store the value that will be used as the Index. The value of V17 will be initialized to 1 (specified in the From field), then each iteration of the loop will increment that value by 1 (as specified in the By Step field) to a maximum value of 10 (as specified in the To field).
The Calculate Expression (MATH) instruction will add the value in D0 to the value in location D[V17]. The first time through the loop V17 will contain the value 1, so the MATH instruction will calculate D0 = D0 + D1.
The next pass through the loop V17 will be 2, so the MATH instruction will calculate D0 = D0 + D2. This process will continue with D0 = D0 + D3 ... until it calculates D0 = D0 + D10.
Since the loop operated 10, and 1 was added each time, the result in D0 will be 10.
|
|
|
Sample Application: One Dimension Table
Create a new data block, named TempSample, of the required data type, in this example select Signed Word.
The data block should have enough capacity to store the required number of samples, in this example enter 100.
Notice the Block Range and Retentive Range fields show the new controller elements (TempSample0 - TempSample99) that will be available for use after this operation is complete. |
|
|
|
The ladder logic to utilize this new data type as a one dimension table follows:
|
|
|
|
On the rising edge of each Trigger input, and as long as the current number of samples stored is less than the maximum number of samples that can be stored ...
|
|
|
Sample Application: Recipe ManagementAssume that the Do-more controller needs to store multiple recipes, each with multiple ingredients, and provide random access to them at runtime. Expanding the one dimension table example to include multiple one dimension tables, this can be done quite effectively.
Each of the data blocks should be large enough to hold the maximum number of recipes.
In this example there are eight new data blocks created, of varying types, with each capable of storing 32 elements.
|
|
|
|
Providing random access to a recipe at runtime is done through a V memory location that is used as the 'recipe pointer'. To access the elements of a specific recipe do the following:
Set the contents of
Use the required Print to String (STRPRINT) and Move Value (MOVE) instructions to copy the 'pointed to' values from the recipe data blocks to the memory locations in the controller where they are used in the project.
This example copies the 'pointed to' elements of RecipeName, RecipeA, RecipeB, RecipeC, RecipeAddSalt, RecipeHeatTime, RecipeCookTime, and RecipeCoolTime to their respective destination locations in the controller. |
|
|
See Also:
|
|
|
Related Topics:
|
|
|