Author Topic: thermopcouple f4-08-thm-n  (Read 16607 times)

Harvey

  • Newbie
  • *
  • Posts: 7
thermopcouple f4-08-thm-n
« on: March 16, 2010, 09:23:33 AM »
New to direct soft.  I need to drive the input high if there a thermocouple is disconnected or shorted. any ideas

Gene Bond

  • Newbie
  • *
  • Posts: 5
Re: thermopcouple f4-08-thm-n
« Reply #1 on: March 16, 2010, 08:30:19 PM »
Forgive me, but I've not used this card, but couldn't you do do a couple of compares that are out of your normal range for alarms? Seemsif the T/C is shorted, the register would read very low, surely lower than normal for the process, and if it's open, it should read very high...

Again, maybe not applicable, but it may help.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: thermopcouple f4-08-thm-n
« Reply #2 on: March 16, 2010, 10:10:31 PM »
The manual defines that there are "Broken Transmitter Bits".

As far as 'shorted', Gene's suggestion to test against any possible normal measurement is a good one. Be aware though that a shorted thermocouple - the two leads shorted together at some place other than the normal measuring end - will measure the ambient temperature at the shorted point.
An output is a PLC's way of getting its inputs to change.

Harvey

  • Newbie
  • *
  • Posts: 7
Re: thermopcouple f4-08-thm-n
« Reply #3 on: March 17, 2010, 07:56:35 AM »
Open it is reading low, if I unwire the t/c it will read 92 deg what I would like this be a read high so the heater does not keep trying to heat.  Other plc cards I have used have a way to configure this; I have not worked much with direct soft.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: thermopcouple f4-08-thm-n
« Reply #4 on: March 17, 2010, 08:49:37 AM »
I repeat:

Quote
The manual defines that there are "Broken Transmitter Bits".

It's not a function of Directsoft. It's a function of the thermocouple card. Read the instructions carefuilly.

An output is a PLC's way of getting its inputs to change.

Harvey

  • Newbie
  • *
  • Posts: 7
Re: thermopcouple f4-08-thm-n
« Reply #5 on: July 31, 2010, 01:43:57 PM »
 yes it is "Broken Transmitter Bits"in on the f4-08thm not the -n. On the f4-08thm-j card it is to go high same as burned out thermocouple this is staying at 95 deg when the termocouple is unplugged. 

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3607
  • Darth Ladder
Re: thermopcouple f4-08-thm-n
« Reply #6 on: July 31, 2010, 01:53:05 PM »
There is no F4-08THM-N listed as a part number on the website.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: thermopcouple f4-08-thm-n
« Reply #7 on: July 31, 2010, 02:37:16 PM »
The 'F4-08THM-N' is a shorthand for either of the older cards F4-08THM-J or F4-08THM-K which were single single type thermocouple specific. The (I believe) newer F4-08THM accepts a variety of thermocouples.
An output is a PLC's way of getting its inputs to change.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3607
  • Darth Ladder
Re: thermopcouple f4-08-thm-n
« Reply #8 on: July 31, 2010, 04:11:24 PM »
Oh, sorry, I assumed it was a module specific to Type N thermocouples analogous to the J and K-type cards.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

Harvey

  • Newbie
  • *
  • Posts: 7
Re: thermopcouple f4-08-thm-n
« Reply #9 on: August 02, 2010, 09:22:36 AM »
My understanding is with the F4-08THM card you can set up each channel for a different type of thermocouple with a jumper, thank you for all the help and input.   :D