News:

  • November 22, 2026, 08:41:11 PM

Login with username, password and session length

Author Topic: Powerflex 525 Output Frequency Drops Out  (Read 26688 times)

TAS

  • Newbie
  • *
  • Posts: 1
Powerflex 525 Output Frequency Drops Out
« on: March 06, 2024, 11:31:19 AM »
My Powerflex 525 VFD "Output Frequency" starts to drop out (20, 19, 18, 17, 16, 15, 14, 14, 0, 13, 0, 12, 11, 10, 0, 9, etc.) when the Command Frequency approaches and falls below approx. 14HZ. The "Command Frequency" however does hold steady and does not drop out (20, 19, 18, 17, 16, 15 14, 13, 12, 11, 10, 9, etc.). The Pulse In Scale is set to 64.

I'm using the Pulse Train Input, and as a test started the frequency of the Pulse Train Input at a frequency such that the Command Frequency started at 20HZ, and then slowly adjusted the frequency of the Pulse Train Input down such that the Command Frequency decreased down towards 0Hz.

I did notice that this apparent drop out point is exactly one tenth of the Max Hz value. So for example, with Max Hz set to 140, the dropout starts to occur at approx. 14 (140 x 0.1 = 14). This apparent one tenth drop out point held true for other Max Hz values we tried, including:

Max Hz set at 60 started dropping out at 6

Max Hz set at 100 started dropping out at 10

Max Hz set at 140 started dropping out at 14

Max Hz set at 180 started dropping out at 18

Max Hz set at 190 started dropping out at 19

Max Hz set at 200 started dropping out at 20

Max Hz set at 250 started dropping out at 25

Max Hz set at 400 started dropping out at 40

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Powerflex 525 Output Frequency Drops Out
« Reply #1 on: March 06, 2024, 12:20:53 PM »
I think that's an Allen Bradley product.  Host Engineering does not develop that.  Rockwell Automation can probably help you a lot more than this forum (although some of our customers also use AB products).