News:

  • September 29, 2023, 04:10:00 PM

Login with username, password and session length

Author Topic: Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor  (Read 154 times)

ZoNiE

  • Newbie
  • *
  • Posts: 5
Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor
« on: September 17, 2023, 12:28:58 PM »
Hi folks. We are looking to use two of our unused inputs on a BX-08THM for Transducer input from an Automation Direct QPSL-AN-42 Pressure Sensor primarily to read vacuum.
It looks like we can just use a 56ohm resistor across the inputs to get a 0.224V to 1.120V range when using the 4-20mA output of the Sensor.

We'll effectively get 4-12ma range below 0 PSI which I think the range will be enough for us. (0.224V to 0.672V, 0.448v of range).

I just wanted to be sure this is OK before I fry a $270 module.

The alternative is to add an analog module that is currently backorderd and $230, Plus the space and bus current needed for it.

I've converted 4-20 to 0-5V using a 240ohm resistor before, but this was with a different control system (An Arduino, actually).

If this will work, it would be great.

Any help is much appreciated.
« Last Edit: September 17, 2023, 12:52:03 PM by ZoNiE »

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 668
  • Why for you bury me in the cold, cold ground?
    • Host Engineering, Inc.
Re: Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor
« Reply #1 on: September 18, 2023, 04:06:01 PM »
The input impedance of the BX-08THM module is >1M-ohms. So, if you select to configure that particular analog input as 0-1.25VDC range, then the voltage drop across the 56-ohm resistor should easily fall within that range (as you pointed out; 0.224 to 1.12 volts).

This should work.
There are two types of people in the world; those that can extrapolate from incomplete data sets.

ZoNiE

  • Newbie
  • *
  • Posts: 5
Re: Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor
« Reply #2 on: September 18, 2023, 04:50:54 PM »
Hi Greg, Thank you for the quick reply.

Do I need to tie (-) to ground or is it already done so internally?
« Last Edit: September 18, 2023, 04:52:57 PM by ZoNiE »

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 668
  • Why for you bury me in the cold, cold ground?
    • Host Engineering, Inc.
Re: Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor
« Reply #3 on: September 19, 2023, 09:45:48 AM »
That's a good question. The BX-08THM is a FACTS Engineering design (not ours at Host Engineering). Our hardware engineers said FACTS Engineering's spec sheet for this module says 0 commons. This makes us think there is no channel-to-channel isolation. Common mode range is limited to 0.6VDC. So that basically means that the TCx- nodes all need to stay within 0.5VDC of each other. From their spec sheet, it is not clear if there is any isolation from user supply 0VDC to TCx- nodes.

So, the bottom line is, you probably need to ask FACTS Engineering to be sure. Sorry.  :(
There are two types of people in the world; those that can extrapolate from incomplete data sets.

ZoNiE

  • Newbie
  • *
  • Posts: 5
Re: Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor
« Reply #4 on: September 20, 2023, 09:24:44 PM »
Ahh. Though all BRX were yours. I see them on their site now. Their modules should remain white.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 5922
  • Yes Pinky, Do-more will control the world!
Re: Using BX-08THM inputs for QPSL-AN-42 Digital Pressure Sensor
« Reply #5 on: September 21, 2023, 07:36:39 PM »
Ahh. Though all BRX were yours. I see them on their site now. Their modules should remain white.

Host makes the -3 and UT analogs. FACTS make the rest.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO