News:

  • November 22, 2026, 10:59:33 PM

Login with username, password and session length

Author Topic: BX-DM1E-10AR3 program err  (Read 26110 times)

pbw

  • Hero Member
  • *****
  • Posts: 127
Re: BX-DM1E-10AR3 program err
« Reply #15 on: July 21, 2023, 09:38:08 AM »
Update: I Updated the PLC Firmware, reconnected and I was able to read the Program from it.
Looks Good!
Thanks for your help.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: BX-DM1E-10AR3 program err
« Reply #16 on: July 21, 2023, 09:58:48 AM »
Update: I Updated the PLC Firmware, reconnected and I was able to read the Program from it.
Looks Good!
Thanks for your help.

You mean you updated Designer software (not PLC firmware, although that's also important but for other reasons).  Designer 2.9.1 had a bug in it that misreads your program in that one rare situation when Designer reads it back from the PLC.  Designer 2.9.2 addressed that issue.  Make sure you are running the latest Designer software (2.9.4) and not 2.9.1 (Help->About in Designer software).

pbw

  • Hero Member
  • *****
  • Posts: 127
Re: BX-DM1E-10AR3 program err
« Reply #17 on: July 21, 2023, 11:45:30 AM »
I was running Designer 2.9.1.....downloaded and installed 2.9.4....then updated PLC firmware...disconnected from PLC...reconnected, and then I was able to read the project from the PLC.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: BX-DM1E-10AR3 program err
« Reply #18 on: July 21, 2023, 12:22:00 PM »
I was running Designer 2.9.1.....downloaded and installed 2.9.4....then updated PLC firmware...disconnected from PLC...reconnected, and then I was able to read the project from the PLC.

PERFECT!