News:

  • October 14, 2026, 01:16:45 PM

Login with username, password and session length

Author Topic: Modbus RTU via H2-ECOM  (Read 12851 times)

Elecnut33

  • Newbie
  • *
  • Posts: 8
Modbus RTU via H2-ECOM
« on: May 13, 2009, 02:19:13 PM »
I have a DL260 processor and I am trying to communicate (H2-ECOM-100) with an Altivar 31 via modbus(RTU) RS485. I have a Connexium TSXETG100 ethernet gateway that I am using to convert the ethernet comms to the RS485 modbus. I cannot seem to get the commands through to the inverter.

Can anyone offer any advice or sample programs that might explain how to do this?

Thanks.

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 702
  • Hmmm...
    • Host Engineering, Inc.
Re: Modbus RTU via H2-ECOM
« Reply #1 on: May 15, 2009, 04:17:54 PM »
The H2-ECOM100 has to be configured using NetEdit (free software). The H2-ECOM100 has to have a Peer-to-peer table in it that points to the Connexium TSXETG100 ethernet gateway's IP address. Then you use the RX/WX (or IBox ECRX/ECWX) instructions in the DL260 to read and write.

Also, the H2-ECOM100 does true Modbus TCP, not Modbus RTU on TCP.
There are two types of people in the world; those that can extrapolate from incomplete data sets.