I am looking at possibly going to a TC transmitter that with split the signal, mV/4-20mA. I was trying to keep away from the scaling issues associated with that.
Answering a few questions in Replies:
There is nothing that happens at 1250, that is just where it seems to happen.
The input value at the Eurotherm CR holds at 1250 and continues to climb as heat is applied. There are also 9 other TC's hooked to the Chart recorder in zones inside.
At one point, I got the Fluke control meter, and plugged in the TC I unhooked from PLC, it read accurately, and I dialed in an output on the Fluke and the PLC read correctly. This really baffled me... Its almost like the BX-04thn went into some shutdown mode...
Agree to Agree that daisy chained TC's are just asking for trouble. This thing has been a PITA since it was delivered. I'm coming in 4 years into the nightmare that is this furnace. I figured I would wave my magic PLC wand, and everything would be fixed. I must have forgot to renew my PLC magic wand policy.
The weird part is, I had a TC directly coupled to PLC that exhibited same/similar issues. that one is now on a single loop controller as my overtemp safety.
This morning after it cooled down from yesterdays test, I found the - TC wire up on top was loose, I fixed it to the junction block good and tight and restarted my cycle.
One of the biggest problems is, i have a 4 hour heat up, if anything goes awry, I cant work on a 1200+ degree oven until it cools, which is the next day. Of course, this is the hard part to explain to the boss...