« on: September 10, 2021, 02:35:23 PM »
I need to read and write to some registers in a ML1100. The serial port of the ML1100 is connected to an HMI and configured for DF1. I have been told that the 1100 will not do MODBUS TCP. Does anyone have any recommendations? Will Ethernet IP work? Your help is greatly appreciated.
Thanks, Mike

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: DoMore to MicroLogix 1100
« Reply #1 on: September 10, 2021, 04:57:45 PM »
I don't have first hand experience, but it looks like from the below post you can probably get Explicit EIP to work with it.

https://www.reddit.com/r/PLC/comments/ago2xr/pc_micrologix_1100_plc_readwrite_tags/

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: DoMore to MicroLogix 1100
« Reply #2 on: September 21, 2021, 08:31:14 PM »
I was unable to get Ethernet/IP to work. I only had three addresses to exchange so I used a Cmore as a interface between the two.